434.5.1.
I'll have a go and try and explain this for trainees.
In the event of an overload scenario (as opposed to a high current short duration fault such as a short circuit), we understand that a device can be reset and will operate within it's design parameters because typically the fault is less than the rated breaking capacity of the device. Considering a typical BS EN 60898 circuit breaker, the rated breaking capacity is 6000A.
Interrupting any fault current under this, SHOULD mean the device will suffer no damage and can be returned to active service. Clearly interrupting say a 40A overload on a 32A device should present no problem and the device should continue to meet it's design specification for a considerable period of time. Sure there may, if there is repeated tripping under such an overload, be slight contact degradation that can result in a high resistance contact and ultimately device failure, but overall the device should be fine.
Now consider short duration high current faults, say line to earth (on a TNCS or TNS system) or line to neutral short circuits.
With good earthing, it's easy to achieve prospective fault currents in these situations of over 1000A. Clearly breaking a fault of this magnitude is an entirely different kettle of fish. If the installation is very close to the substation or is three phase (or both), it's entirely possible to have situations where the prospective fault is over 6000A.
When a protective device tries to break a fault current that is larger than it's rated breaking capacity various things can happen....
In the case of a fuse, the fuse element could break and then if the fuse itself doesn't meet specification, it could continue to arc internally, ultimately resulting in an explosion of hot plasma and molten metal. This is why high rupture capacity (HRC) fuses are filled with special sand... to extinguish the arc.
In the case of a circuit breaker, it could explode or suffer internal damage (that may not be visible to the user). The internal damage may mean it no longer operates within parameters, if it operates at all, or it may result in a more catastrophic failure if it were to be closed on a fault.
@pc1966 posted a video about devices being tested within their specifications but which failed... badly... if you've not watched it, go and do so because it's a good primer on why you should never just re-energise a tripped breaker (
Another video on fuses versus MCCB - https://www.electriciansforums.net/threads/another-video-on-fuses-versus-mccb.193572).
So... this regulation formalises this requirement by specifically stating the short circuit breaking capacity of protective devices must be larger than the prospective fault current. Providing the devices comply with this requirement, you should in the case of a circuit breaker at least be able to reset them and leave them in service. If it's found that the prospective fault current is larger than the breaking capacity of a device, the device should be replaced at your earliest convenience with one that has the required capacity.
Now, someone can have a punt at
433.1.204