Go on then.Now, someone can have a punt at 433.1.204
Go on then.
433.1.204
Accessories to BS1363 may be supplied through a ring final circuit, with or without unfused spurs protected by a 30A or 32A protective device [ BS88 fuse / MCB / RCBO meeting relevant regs ]
The circuit shall be wired with copper conductors having line and neutral conductions with a minimum cross sectional area of 2.5mm sq. except for two-core mineral insulated cables complying with BS EN 6072-1 for which the minimum cross sectional area is 1.5 mm sq. Such circuits are deemed to meet the requirements of 433.1.1 if the current carrying capacity (Iz) of the cable is not less than 20A and if, under the intended conditions of use the load current in any part of the circuit is unlikely to exceed for long periods the current carrying capacity (Iz) of the cable.
This describes the good 'ole British ring final circuit and explains several things.
In certain circumstances you can do something which would normally not be allowed - you can use a 30/32A OCPD with 2.5mm T+E cable. As the best possible current carrying capacity is only 27 amps (clipped direct, table 4D5) and this is less than 30/32A it does not meet reg 433.1.1. However the exemption is permitted if certain conditions are met:
- obviously it must be wired in a ring, allowing the load current to be balanced on the two legs.
- the circuit must supply 13 amp sockets / plugs / fused connection units (BS 1363 accessories)
- the tabulated current carrying capacity in table 4D5 for the method of installation needs to be at least 20 amps. Methods 101 and 103 do not meet this requirement, so a cable over a plasterboard ceiling in >100mm thick insulation or a cable floating inside an insulated stud wall shouldn't be used as part of a ring final circuit.
- the load current at any point in the ring (and spurs if any) shouldn't be expected to exceed the current carrying capacity of the cable used for long periods of time.
[1.5mm mineral insulated cable can be used too, refer to table 4G1A]
Improvements on this attempt welcome!
I'll throw up 411.1 for next punter.