OP
Dickylad
Hi,
looking at a blown up photo of the contactor it appears to be a 24V AC coil (TeSys K CONTACTOR 4kW 9A 24VAC) so to test contactor wire from 24V (transformer) to A1 (contactor) and 0V (transformer) to A2 (contactor) and it should pull in. If you have wired it in the past so 600V went across the coil it may have burnt out. Hope this helps,
Regards,
Dickylad.
looking at a blown up photo of the contactor it appears to be a 24V AC coil (TeSys K CONTACTOR 4kW 9A 24VAC) so to test contactor wire from 24V (transformer) to A1 (contactor) and 0V (transformer) to A2 (contactor) and it should pull in. If you have wired it in the past so 600V went across the coil it may have burnt out. Hope this helps,
Regards,
Dickylad.