Hi,
looking at a blown up photo of the contactor it appears to be a 24V AC coil (TeSys K CONTACTOR 4kW 9A 24VAC) so to test contactor wire from 24V (transformer) to A1 (contactor) and 0V (transformer) to A2 (contactor) and it should pull in. If you have wired it in the past so 600V went across the coil it may have burnt out. Hope this helps,
Regards,
Dickylad.
 
On the side of the contactor it does say 600v max. Can't see where it states the coil rating though, as it has 24v on the front i'm assuming its that. Dickylad tried that and still no joy, so guessing its kaput!
 
Last edited by a moderator:
Hi,

Measure the resistance of the coil. Check the resistance of the Foot pedal switch. It does sound like the Coil is kaput. You really need to verify the correct coil operating voltage. Ohm out the wiring when you replace the contactor. What ever the operating voltage of the coil requires, put that to terminal 3 on the foot pedal switch, the other side of the switch terminal 4 on the foot pedal to A1 of the contactor, A2 to neutral. The contactor should pull in then. This is assuming the foot pedal is a NO switch, which it should be.
When you depress the Contactor you should get contact between both sides of the contactor, L1 to T2 etc..
 
Last edited:
Hyperliteliam,
thought I would draw up how I think your circuit should look. I have used red and black for the 600V so you dont confuse them with the other blue and browns running horizontally. It may or may not be of any use, I haven't shown fuses in the 24V or 600V circuits,

Regards,

Dickylad

[ElectriciansForums.net] Bit of help ASAP.....Please!!
 
Thanks for the drawing dickylad, really appreciate it. Gotta be honest and say this is my first real go at 'panel building' if you like, so bit green really with it all.
Basically the father in law had to buy this as a kit because Kellys (turkey people) weren't allowed to sell it complete as its over 150 volts apparently. Their 'electrician' designed this as their previous stunner was not as safe as this design apparently, so can't see why these appropriate fuses haven't been included.
So to make this all ok what fuses are required as i'll pick these up with the contactor..

Thanks again guys
 
Evening guys.

Got this working the other day. 600v present at the stunner probe commando socket when foot-pedal pressed.
But got a slight problem; i think...?
As i've stated, when i check voltage at the commando socket i've got 600v and the contactor pulls in fine, but when i plug in the probe to the socket then press the foot-pedal the contactor rapidly pulls in and out, in and out till i press the button on the probe.
When the button on the probe is pressed the contactor stays pulled in...

Is really puzzling, anyone shed some light on this for me please...

Cheers
 
Yeah I am for real mate. Is that alright.

Looks like I ALSO forgot that i should have contacted you about the problem I've had in the first place, sure you would have sorted it well quick.

Do one mate, this ain't what this forums about. Seems you'll be more suited to the screwfix forum after the above constructive reply....
 
Hi hyperliteliam,
if the contactor is bouncing in and out it must be an issue with what is controlling it i.e. the foot switch. Are you getting a clean 24V AC onto the A1 and A2 of the contactor? Don't worry about other people having a go we are all at different levels, I am sure there are lots of things you can do better than me, anyway check for a good connection on your pedal switch, hope this helps,

Regards,

Dickylad.
 
Something else I have thought about, if when you have the probe connected the contactor bounces in and out, it may be a fault or the size of the probe is too big for your transformer. This may occur due to the probe pulling the voltage down which because of the shared transformer the 24V AC for the contactor could be pulled down below the value which will hold the contactor in so it drops out, when it drops out the voltage recovers and then the contactor pulls in again, this could result in what you describe. Have you fused the 600V and 24V circuits?
Regards,
Dickylad.
 

Reply to Bit of help ASAP.....Please!! in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
220
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
836
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
830

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top