Just pricing up extension with a fair bit of external electrics.

The part which I need a hand on is:

9 x outside wall lights around building (not decided on what type / wattage etc)
4 x PIR wired in parallel to control these (one on each corner)
2 x over-ride switches inside

Been looking on Steinel website @ IS300, just not too sure on the technical bit - will it work..... if I read it correctly it states that

- 2000 W max. (resistive load, e.g. filament bulb), - 1000 W max. (uncorrected, inductive,
cos φ = 0.5, e.g. fluorescent lamps) - 1500 W max. (series corrected) - 500 W max. (parallel corrected, with C ≤ 45.6 μF) - electronic ballasts, capacitive,
e.g. low-energy lamps, max. of 8 each. C ≤ 176 μF
3-sensor technology of the IS 300

So limited to 50w / light, but it also states that you can only use 8 low-energy lamps ? So cant go down that route or can I ?

And will 4 PIRs normally work in parallel with each other, have done it 2 in parallel but never 4 ?

Help / advice please

Many Thanks,

Sy
 
No problem with using the 4 PIRs in parallel, just have to watch the loading. Assuming that all lights come on when one PIR is triggered. If it's a dedicated outside light circuit you could consider using a contactor if the loading is a problem.
 
No problem with using the 4 PIRs in parallel, just have to watch the loading. Assuming that all lights come on when one PIR is triggered. If it's a dedicated outside light circuit you could consider using a contactor if the loading is a problem.

Thats the answer i was looking for - thank you very much, my brain is so overloaded with figures at the minute didn't even think of that.

Nice little contactor unit, everything going back to there, dedicated circuit in and no worries about overloading the PIRs

Sy
 
Not sure if it's this make, but my brother as a system on his house that is similar which I wired up for him and it as all sorts of add ons for CCTV and integrated into the house alarm.

I'm not sure how much it was but he was forever standing behind me making sure I was doing it right, so as he is a tight wad I would imagine it was pricey mate.

Just thought it might be something to think about.
 
but he was forever standing behind me making sure I was doing it right,

Bet that wasn't annoying :30: I had a watcher this week..... "is that the normal way of running cables, I thought they all came from above..." (I was bringing them in from below) Urghhhh !! :banghead:

Thanks for your help chap - but think will go down the contactor route this time as know what I'm doing there. The other system looks like it has more potential for me to cock it up and trying to keep costs down (although struggling at the minute)
 
I do always give the customer the choice... get yourself a nice B&Q special flood light with pir for £25 (and I'll charge when I pop back when it goes wrong...)

or I'll get you a steinel for £80 and guarantee it for 3 years

Steinel every time (I hope you don't think I'm on commission or something)
 
Nope lol I've just put in one of the small 150w floods ceramic heat shield cast alu housing nice bit of kit. I want to put in one of those LED floods they've got but no one will pay £190 plus VAT:icon9:

just seen they've bought out a new one thats 14.8 watts for £79 plus the vat getting more reasonable
 
Last edited by a moderator:
if you are going to use a contactor, you may have to fit a capacitor across the coil as the inductive load of the coil can cause problems with the PIRs. something in the region of 0.1 - 0.5 mfd.
 
if you are going to use a contactor, you may have to fit a capacitor across the coil as the inductive load of the coil can cause problems with the PIRs. something in the region of 0.1 - 0.5 mfd.

Right I didn't realise that thank you Tel. Never used a capacitor before, how do calculate what size/type required please ? and what would be 0.1 - 0.5mfd (bit too technical for me sorry) Last think I want to do is wire it all back there and it dosent work out as planned
 
led is prob best with pir-but pricey

incandescent you've a bit of maintenance with bulbs

cfl -the short on-time reduces lamp life ,and like you say there's a limit on the no. of ballasts that can be switched 'direct'

photocell is so much simpler:)
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

sythai

Arms
-
Joined
Location
Devon, United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Bit of help please....if possible
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
sythai,
Last reply from
telectrix,
Replies
15
Views
1,746

Advert

Back
Top