1shortcircuit

Firstly, please let me explain the fault on the circuit HAS been rectified. This was achieved by splitting the offending circuit (kitchen ring) into two radials and putting each leg on their own 16A mcb on the same RCD.

Attended a property to do some remedial works on the kitchen ring, New dual RCD protected board already installed and just there to put rubber grommets into back boxes. Such a joy:tongue3:

Anyway as I always test circuits before working on them I found a dead short between Neutral and Earth but RCD holds?

RCD tests came back well within specified tripping times on x1 and x5 tests but RCD failed to recognise this dead short?

Anyone have any suggestions as to why this RCD will test fine but not do it's job as intended?

All testing was done with circuit completely removed from Consumer Unit. Faulty leg found between two sockets so removed and as said made ring into two radials, each on their own mcb (same RCD). Comment sticker left on consumer unit explaining circuits 2 & 3 both energise kicthen.

Kind Regards

1SC
 
The thing is what lessons should be taken from this well yep you have a low reading but at the same time it costs nothing to do some other tests as well even if you just jott them down a bit like a British Gas guy who tests a socket and says big problem here you have no earth but if he tested some other sockets ie random he may have said this socket has no earth but the others are ok
 
I would suggest neutral on the faulty leg is interconnected with a neutral of another circuit (likely to be cooker). I am assuming you only removed the circuit in question to carryout the testing. Therefore leakage back through other neutral to earth at transformer. I would suggest removing faulty neutral and carrying out test between that and the neutrals of the other circuits on that RCD.
 
I would suggest neutral on the faulty leg is interconnected with a neutral of another circuit (likely to be cooker). I am assuming you only removed the circuit in question to carryout the testing. Therefore leakage back through other neutral to earth at transformer. I would suggest removing faulty neutral and carrying out test between that and the neutrals of the other circuits on that RCD.

I've tested for borrowed Neutrals between other circuits as this is what I first suspected. Also, whilst the circuit was removed I tested for continuity of both Neutral legs to the main earth bar of consumer unit and nothing :thumbsup

Does it the circuit trip under load?

Nope, not a single trip and circuit has been under normal daily usage

Thanks for all your help everyone, much appreciated as always.
 
Erm, quite possibly?

So whilst the IR reading was low enough to require further investigation and rectification there may have been enough resistance between Neutral and Earth to not trip the RCD.

The thread title is "bizarre dead short"we will have to call you 2shortcircuit from now on :smile:
Your reading has only confirmed that you dont have a million ohms,add a bit of resistance of the cpc back to the met and its not that bizarre I would say for the rcd to hang on in there
 
That will be fine just write down for 'Design ' Electrical Trainee and Signed of by NICEIC supervisor ..Of course I am being flippant..? ' Tony Cable'..my autobiography I woke after 5 weeks from a coma...To find myself as an Electrician lol
 
The thread title is "bizarre dead short"we will have to call you 2shortcircuit from now on :smile:
Your reading has only confirmed that you dont have a million ohms,add a bit of resistance of the cpc back to the met and its not that bizarre I would say for the rcd to hang on in there

It would seem you have hit the nail on the head.

The earth leakage is obviously working within the tolerance of the 30mA RCD therefore not tripping it however at a later date this could become worse and lead to nuisance tripping or the amount of leakage combined with that of other circuits could eventually step out of the tolerance level again causing nuisance tripping.

At least my actions of finding and rectifying the fault were correct and should eliminate any tripping of the device.

**** note to myself, Learn more, test more and understand more ****


Thanks again to everyone that has added their input, great forum.... I continue to learn more everytime I log on:thumbsup
 

Reply to Bizarre dead short between Neutral and Earth in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
315
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
954

Similar threads

Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
383
Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
758

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top