G
Gossy
I have installed a new cooker supply to the new DB. The cable is a 10 mm T+E. It's on a 50 amp RCBO. (Big cooker!!) tested the cable and made put it in connector block and switched it on. I was getting 240v down live to earth which is correct but neutral to earth is was getting 40v. Then live to neutral I was getting 118V . I thought it was thought it was the RCBO but changed it three times and still read the same. When I connected it to cooker I get 240 v through neutral and earth as well as live and earth. What's going on???