Wonder if I can get some guidance, on max demand in block of flats. It always was hard for me as it always comes to massive demands, and I red here that it all comes with years of experience and that it is like an art. This is first bigger project I am taking on. So please don’t shoot.

I need to determine the max demand for the job, so the correct supply can be brought in.

Basically it is an old mansion being converted to a block of 11 flats.

Each flat will have: 2 lighting, 2 ring, 1 shower 8.5kW (37A), 1 cooker 4.5 kW (19.6A).

Option 1: Going by OSG diversity: 4A lights+4A lights+32A ring+8A ring+37A shower+16A cooker=101A (crazy)


Option 2: Going by 0.4 factor diversity: (6+6+32+32+37+19.6) x 0.4 =53A (more like it)


For the whole house:
Can I treat flats as circuits in this instance and apply 0.4 factor again? Then:

Option 1: ((101A x 11)+ 20A landlords board) x 0.4 =452A (3Ph), Supply current per phase 452/3=150A. So I need then 103.5kW 3ph+N supply.


Option 2: ((53A x11) +20A landlord board) x 0.4 = 241A (3ph). Supply current per phase 241/3=80A. So I need then 55.2kW 3ph+N supply.

I find myself thinking to come up with Option 3, :banghead:: (option 1+ option2) /2. =80kw 3ph + N supply.

So what you think? Am I somewhere near with my thinking? Obviously if I can’t work it out I will go with safest but unfortunately most expensive option 1, it just seems it will be rather large supply cable 50 mm2 or maybe higher, it is what it is I suppose. Not sure about ratings on supply cables, just had a look in regs book, 50mm2=135A and 70mm2=167A, SWA XLPE reference D, obviously its different cable.

After and if I will get this confirmed by more experienced, I then will share with my calcs and plans of action for the customer’s installation.

Thanks in advance for your help and guidance.

Al
 
Last edited:
Re flats: Generally now all meters to each flat have to be on the ground floor altogether in a community room whereby each tenant/ owner has 24 hour access. The DNO would have to install a suitable sized mains cable (possibly 95cne) into a Ryefield box to cater for 11 flats plus "Landlords supply" for corridor lighting and fire alarm. From the Ryfield box a separate cable to a 60/80amp cut out (header) fuse is supplied for each flat. The supplier will the connect a separate meter to each and every flat. A suitable sized switch fuse is then fitted by the electrician, running a separate sub main to each flat consumer unit. To accommodate all the DNO's equipment , meters, switch fuses etc a large area is required. Basically all the cut -out fuses and meters are next to each other along with the switch fuses.
 

Reply to Block of flats. Max Demand in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
325
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
852
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
973

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
779

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top