gerard

Hi,
I work as a Maintenance Electrician in a factory and when one of the guys there told me he has a problem with blowing bulbs, I had no answer for him! He told me a bulb will last about 2 days and then blow. Has anybody ever experienced such a problem and what may cause it? :banghead:
 
I reckon so as well

I always used to tell people " dont get your lamps from Woolwoths"
Now that their shut, I need to find another fall guy
[ElectriciansForums.net] Blowing light bulbs!
 
The main suspects are:
1) Poor quality lamps.
2) Over-voltage, +5% over-voltage will more than halve the life expectancy.
3) Loose connections.
4) Poor quality lamp holders, particularly batten fittings.
5) Power quality, surges, noise and harmonics all can shorten the life expectancy.
 
Last edited by a moderator:
Is it one particular light fitting or do the bulbs blow anywhere ??
Anywhere then bulbs are likely to be poor quality as previous posts explain.
Is it on one circuit IE up or down ?
One light fitting then it indicates a fault with that fitting replace or at least test for faults particularly Insulation resistance
Bulbs blowing on one circuit but not any other circuit indicates a circuit fault
If its a voltage problem consider fitting a dimmer switch
 
Last edited by a moderator:
Do you order the lamps? What make are they?

One company I worked for the buying department got a great deal from a new supplier (cheap) but we were changing 3 times the number. A 20% saving cost 240% more! What finally clinched it I opened one box and spotted the solder connections had the internal wire protruding through it, then it became a H&S issue.
(Some of the older sparks may remember these cheap lamps coming in from Poland in the late 80’s)
 

Reply to Blowing light bulbs! in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
888
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

My experience with commercial lighting is when the fixture is ordered or bought the specs should say 120/277. Then their wiring diagram should be...
Replies
7
Views
580
  • Question
By the looks of it the whole head comes off in one unit, guess it has a driver inside of it. Ive tried to Google the Image i have, one comes up...
Replies
3
Views
548

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top