Hi all, am going to be doing an inspection on a property which the customer wants a satisfactory report. ie no c1's, c2's. First question Bathroom lighting circut has no 30ma rcd protection, so a C2, next problem lighting circut into bathroom has no Cpc. Can i get around this by installing supplementary bonding in the bathroom?. What does no earth in lighting circuts go down as? C1?. I suspect the board my be a rewire able so possibility of a new board, but how can i give them a satisfactory report? my mind boggles. Thanks
 
The customer dictating how the report will come out? That's a good one. Your report will be what it will be mate, all you can do is code it up and quote for any remedials needed/recommended
 
Is the bathroom upstairs? You might have some luck in a lighting junction box in the attic finding a CPC in there...
 
Well no earthing in lighting circuits goes down as a c3 as long as no class 1 (metallic) fixtures are used and a suitable label fixed at the db. IMO if it has no earth and it has an enclosed ip rated fitting, it would not require supplementary bonding either, although I would wait for someone to confirm/diasagree with this, all other bathroom circuits would require 30ma protection or supplementary bonding.
If you fit a new board just fit an rcbo on the lighting, it will still give shock protection.
 
Depending in age of install I'd say both lack of RCD c3 and lack of cpc to lights c3, as long as no class 1 items and circuit is 2 core throughout. I would recommend to my clients RCD protection & lighting circuit rewire would be beneficial. Is bonding satisfatory ?
 
The customer dictating how the report will come out? That's a good one. Your report will be what it will be mate, all you can do is code it up and quote for any remedials needed/recommended

It sounds to me like a case of "You give me very nice report & later I give you very nice Balti"
 
Hi all, am going to be doing an inspection on a property which the customer wants a satisfactory report. ie no c1's, c2's. First question Bathroom lighting circut has no 30ma rcd protection, so a C2, next problem lighting circut into bathroom has no Cpc. Can i get around this by installing supplementary bonding in the bathroom?. What does no earth in lighting circuts go down as? C1?. I suspect the board my be a rewire able so possibility of a new board, but how can i give them a satisfactory report? my mind boggles. Thanks

Graham, have a read through the guide below, some of your code suggestions are rather strange and how would installing supplementary bonding allow you to 'get around' the lack of a CPC to a lighting circuit?

http://www.esc.org.uk/fileadmin/use...y/best_practice/BestPracticeGuide4-Locked.pdf
 
I was under the impression that if you had a lighting circuit which did have a cpc, then you could install supplementary bonding and you would not require rcd protection. But im not sure about lighting circuit with no cpc, is their no alternative to a rewire of that circuit?
 
I was under the impression that if you had a lighting circuit which did have a cpc, then you could install supplementary bonding and you would not require rcd protection. But im not sure about lighting circuit with no cpc, is their no alternative to a rewire of that circuit?

Candles perhaps? :clown:
 

Reply to Board Change, satsifactory report in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
319
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
846
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
968

Similar threads

Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
Replies
2
Views
715
  • Question
If they got a shock then something cannot have been isolated.
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top