this is the board change i said i was on with this morning:
this is the intake arrangements for the 4 flats
getting a Ze=0.09
the existing 4 way BS3036 board
old board removed & finals broken out ready for IR and (R1 R2)
(R1 R2) at the furthest point on the lighting circuit=1.28
new board going on
new board straight & level minus cover
a closer look
all dead testing has been done....IR was good...the lowest came back at
18 meg with nothing borrowed/shared ...now ready for the cover to go on & energise....Zs & RCD then sticker up and clean any mess made before leaving....
this is the intake arrangements for the 4 flats
getting a Ze=0.09
the existing 4 way BS3036 board
old board removed & finals broken out ready for IR and (R1 R2)
(R1 R2) at the furthest point on the lighting circuit=1.28
new board going on
new board straight & level minus cover
a closer look
all dead testing has been done....IR was good...the lowest came back at
18 meg with nothing borrowed/shared ...now ready for the cover to go on & energise....Zs & RCD then sticker up and clean any mess made before leaving....