I'm following a spark who used an existing Panel Heater circuit, for new gas boiler circuit 6 months ago. The panel heaters were removed, so it's now a dedicated boiler circuit. I'm doing an EICR.
I've found a number of faults;
1. No grommet in Consumer unit knock out, used for gas bonding (It's a recessed consumer unit)
2. Stranded cable does not have ferrules
3. Unfused Boiler switch
4. 16A MCB (2.5mm T&E)
5. Gas not bonded, bonding taken to central heating pipe only

Most of these are black and white very poor work. I've had to fix all of these so the EICR is a pass, but I have a dilemma.
#4, the MCB is way too big for a boiler. I now have a switched fuse with 3A fuse, so the boiler is now protected. It's a 2.5mm T&E cable so the 16A MCB is protecting the cable. Nothing is unsafe. If it were a new circuit, I'm sure he would have purchased a 6A MCB, but as it's not he's just used existing 16A. I'm going to need to do 16 EICR's following these guys. I'm sure this will be a theme. Is there a reg I can quote for wrong sized MCB, or is this just poor workmanship ?
 
Mcb is not wrong.
up to20A is normally ok for 2.5mm
3A fuse protects fly lead to boiler and associated control cables.
you make no statement about rcd protection, if the cable is buried then it is probably required.
 
In all honesty, I don't know. What is the technical difference ?
Respectfully - if you don't know and understand what you're inspecting, should you be inspecting?
 
1. No grommet in Consumer unit knock out, used for gas bonding (It's a recessed consumer unit)
Are you particularly worried about a bonding conductor touching the frame of a metal consumer unit? Do you feel that is potentially dangerous?

Simpler to add a fused spur (as you did) than mess around changing an MCB for the boiler.
I don't lose sleep about simple fixes, I do them and move on. It's usually quicker than filling out the observations section!
 
While I sympathise with the OP, I would tend to agree with @Rockingit. Anyone involved in periodic inspection and testing of existing installations should be very familiar with the type of installation that they're inspecting and testing.
Of course, no one person can be expected to know everything. But it boils down to the difference between knowledge and experience. Such experience is often picked up on the job whilst working alongside more experienced colleagues.
What though if a person doesn't have the benefit of being able to work with such a mentor?
I suppose the next best thing is this forum...
 
Are you particularly worried about a bonding conductor touching the frame of a metal consumer unit? Do you feel that is potentially dangerous?

Simpler to add a fused spur (as you did) than mess around changing an MCB for the boiler.
I don't lose sleep about simple fixes, I do them and move on. It's usually quicker than filling out the observations section!
My concern was protection against fire, the consumer unit is now open to the cavity. Any internal fire within the consumer unit could now travel freely in the cavity. A blind grommet would have easily resolved this.
 
Is there a reg I can quote for wrong sized MCB, or is this just poor workmanship ?

It's not the wrong size MCB and it's not poor workmanship.

16A 2.5mm radial has been the generally accepted standard supply for any small appliance such as a boiler for a long time.

Using a smaller MCB would be unusual and would be unlikely to give any selectivity with the 3A fuse for the boiler.
 
In all honesty, I don't know. What is the technical difference ?

Coarse stranded conductors do not need ferrules, fine stranded conductors do need ferrules or other suitable treatment at the end.

It is important to remember that the regulations do not require the use of ferrules, they require fine stranded cables to be suitably treated at their terminations. This can be achieved by using ferrules but this is not the only way.
 
My concern was protection against fire, the consumer unit is now open to the cavity. Any internal fire within the consumer unit could now travel freely in the cavity. A blind grommet would have easily resolved this.
A rubber blind grommet wont stop any sort of fire, and regardless this is outside the scope of an EICR.

You are pulling up things that relate to workmanship (gas bond excluded) and adherence to BS7671. An EICR is solely to give an engineering view on whether an installation is safe for continued use.
 

Reply to Boiler circuit 16A MCB in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
393
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
977
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
787
  • Question
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
Replies
2
Views
734

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top