No, No, NO.
Blueflash has it right. I will modify it slightly
L= Live input This must be a permanent live.
LS= Switcched Live supply OUT to remote stat and or controller.
LR= Switch Live Return from stat or remote controller Otherwaise known as the Heat Demand
N = neutral as normal
E = CPC as normal
If you have a remote pump then also there are lines for
Pump live out
Pump nutral
You do NOT connect a permanent live to LS. This is a switched live from the boiler, the boiler switch will switch this on and off. You must use this for your control gear otherwise a service enginear may switch off at the boiler and expect the control gear to be dead.
If your pump is seperate you MUST use the pump live from the boiler. Many modern boilers have a pump override, ie the pump continues working after the boiler has shut down. This is to prevent the heat exchanger from overheating by maintining water circulation until the heat exchanger has cooled to a suitable level. If you are using a three port valve then there will always be a water flow so you need not worry about a bypass, if ever you use two zone valves (plan S) - or just a sinlge some valve for heating only - the zone valve(s) can (both) shut off, so then your plumber will need to ensure a water bypass as well (often the bathroom towel rail).