Hi all, have got to connect up a Y plan central heating system. The diagram seems pretty straighforward but i am a bit unsure about the boiler connections.
i opened up the boiler and there is an: LS, LR and L for connecting a live. LS and LR are joined with a link.
Can anyone tell me where to connect my live to.

Many thank`s
 
Depends on the boiler, is it a combi or back boiler? what make is it? the boilers I normally deal with you take the link out and its just a permanant L - N - E and then a switch live to the boiler. Have you not got the manufacturers instructions to look at?
 
Last edited:
Hi all, have got to connect up a Y plan central heating system. The diagram seems pretty straighforward but i am a bit unsure about the boiler connections.
i opened up the boiler and there is an: LS, LR and L for connecting a live. LS and LR are joined with a link.
Can anyone tell me where to connect my live to.

Many thank`s


hi there, the L is live, the LR AND LS are usually for a room stat
 
Hi guys i am quite ****ed so excuse my reply, the system has a roomstat and seperate timeclock side by side. I was just unsure about wether to connect my live to Live, LR OR LS and to leave the link between ls and lr
 
you ll need to take a five core to the boiler i think connect Lto live and LR,LS back to the roomstat connections on the wiring centre plus N AND EARTH, YOU WILL HAVE TO REMOVE THE LINK.
 
The boiler is not a combi. The plumber told me that the sytem set up is known as a Y plan.
There is a cylinder, cylinder stat and a mid position three port valve. When i look at the wiring diagram there will be a live returning from the mid position valve, through the connections in the joint box and back down to the boiler. Like i said previously where will i connect this live to? Does it just go to the terminal marked L on the boiler and do i leave LS and LR linked

Hi dinga1978, if you look at a Y plan wiring diagram you see one live going to the boiler
 
Last edited:
No....

if the boiler requires a pernament live then the connections will be as follows.

L = Pernament live
N = Neutral
E = cpc

remove the link !! and connect the switch live to LR this is the same wire connected to the orange wire on the 3 port valve.
 
No, No, NO.

Blueflash has it right. I will modify it slightly

L= Live input This must be a permanent live.
LS= Switcched Live supply OUT to remote stat and or controller.
LR= Switch Live Return from stat or remote controller Otherwaise known as the Heat Demand
N = neutral as normal
E = CPC as normal

If you have a remote pump then also there are lines for

Pump live out
Pump nutral

You do NOT connect a permanent live to LS. This is a switched live from the boiler, the boiler switch will switch this on and off. You must use this for your control gear otherwise a service enginear may switch off at the boiler and expect the control gear to be dead.

If your pump is seperate you MUST use the pump live from the boiler. Many modern boilers have a pump override, ie the pump continues working after the boiler has shut down. This is to prevent the heat exchanger from overheating by maintining water circulation until the heat exchanger has cooled to a suitable level. If you are using a three port valve then there will always be a water flow so you need not worry about a bypass, if ever you use two zone valves (plan S) - or just a sinlge some valve for heating only - the zone valve(s) can (both) shut off, so then your plumber will need to ensure a water bypass as well (often the bathroom towel rail).
 
Last edited:
the cables you connect in to LS and LR Will need to be Volt free. make sure there is no voltage on these cables. the voltage comes from the boiler and and is switched via your room stat
 
No, No, NO.

Blueflash has it right. I will modify it slightly

L= Live input This must be a permanent live.
LS= Switcched Live supply OUT to remote stat and or controller.
LR= Switch Live Return from stat or remote controller Otherwaise known as the Heat Demand
N = neutral as normal
E = CPC as normal

If you have a remote pump then also there are lines for

Pump live out
Pump nutral

You do NOT connect a permanent live to LS. This is a switched live from the boiler, the boiler switch will switch this on and off. You must use this for your control gear otherwise a service enginear may switch off at the boiler and expect the control gear to be dead.

If your pump is seperate you MUST use the pump live from the boiler. Many modern boilers have a pump override, ie the pump continues working after the boiler has shut down. This is to prevent the heat exchanger from overheating by maintining water circulation until the heat exchanger has cooled to a suitable level. If you are using a three port valve then there will always be a water flow so you need not worry about a bypass, if ever you use two zone valves (plan S) - or just a sinlge some valve for heating only - the zone valve(s) can (both) shut off, so then your plumber will need to ensure a water bypass as well (often the bathroom towel rail).

Just to add to that thorough explaination. On an S plan if both "lives" are "lost" via the zone valves, boiler will stop as its the only supply on an S Plan/Y plan (although you can configure to use a live feed from "white" valve wire on two port valves.) Usually orange wire. I think the plumbing regs now say no open rads just a dedicated flow to return bypass in pipework.
:)
 
You may find this link to some more explainations and diagrams about boiler connections useful:
Central Heating Boiler Electrical Wiring Connection Diagrams for Electricians | Electrician's Blog
 

Reply to boiler connections in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

I
  • Article
Baxi system boiler and Opentherm Hello Does anyone know if its possible to connect an Opentherm thermostat such as a Nest to a Baxi 800 System...
Replies
0
Views
248
Ian777
I
Certainly is!! And another thing .......... On the old Hive receiver the relay common is a separate terminal, whereas on the new Hive presumably...
Replies
5
Views
368

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top