Hi, currently we have a static caravan with a generator running electric to the caravan. We also have a boiler which lately have been having alot of problems with. Had plumbers out etc but still cuts out. I have an earth stake in the ground with 10mm earth to caravan fuseboard. Testing at the board 230v between live and neutral but 120v from live to earth! Does this mean the earth stake isn't deep enough in the ground or something wrong. Have found out that the boiler Infact needs an earth for it to function properly as has an electronic ignitor. So without a proper earth into the carvan the boiler becomes faulty. I have heard somewhere that generators have a floating earth and some people have said to link neutral and earth at the generator in order to get the boiler working. What other options is there.
 
This is likely to be a problem with the N not being tied to earth.
Have you tested earth loop impedance?
 
Check at the generator to see if the N & E are linked. If you have the manual (or make+model to search on-line) it might say how it is configured.

If you are feeding a single load than an IT (isolated) supply has some obvious safety advantages and allows systems to continue under single fault conditions, but it is not good for more than one load unless fitted with insulation monitoring and under competent supervision (e.g. ship supply, hospital theatre supply, etc).
 
Last edited:
As mentioned above the generator probably doesn't have L-N linked , Iv owned a few small (under 15 KVA) generators and all of them have not had a L-N link. The earthing point on the chassis of the generator just connects to the cpc/earth pins of the outlets,

The earth in this case is basically a bonding conductor and making sure if there is a fault then the earth for each appliances is at the same potential, and the set up is normally isolated from true earth (see attached picture)

It is normally very easy to see if the generator is this configuration by just removing the cover on the part with the socket outlets, obviously with the generator off
 

Attachments

  • [ElectriciansForums.net] Boiler for static caravan - no earth
    Screenshot_20210125-131012_1.png
    994.6 KB · Views: 35

Reply to Boiler for static caravan - no earth in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top