A new. 10k boiler has been installed where there is an existing shower normally i use a RL1 voltage relay but is there perhaps a current sensing relay which can be used instead
Pict
The normal solution is a voltage relay that opens the run signal to the boiler when voltage is present on the shower circuit after the the isolator so I thought that a current sensing relay at the supply source would be as effective without the need for several metres of wiring
I used it for a shower with a different kind of heating load and had a contactor to switch the heating load.
They are very commonly used in Ireland due to the small cut out fuses I believe
Reply to Boiler relay options in the UK Electrical Forum area at ElectriciansForums.net
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...
Hi there , I wired it up following the instructions from similar model. Works great thanks for your help