I have wired many 'c' 's' 'y' plans before but a friend of mine wants system zoning so he can have control over each floor on a combi boiler system (2 floors), Cant think of a simple way of doing this other than adding a relay so there isnt a back feed into the other zone, any thoughts??
I did this with 3 zones - one zone per floor.
I fitted a roomstat to each floor, which operated a zone valve on each floor. Each zone valve was fitted with contacts operated by a cam on the valve spindle which closed when the zone valve was in the open postion, so, when the roomstat caused the zone valve to open (thus allowing water to pass to the radiators on that floor) the contacts on that valve closed & fired the boiler.
This means that if all the roomstats call for heat, all the zone valves will open, & all the contacts on the zone valves close so the boiler fires & all the radiators in all zones heat up.
If however, only one roomstat calls for heat only the zone valve controlled by that roomstat opens, its contacts close, the boiler fires and only the radiators in that zone will heat up.
The same applies if two roomstats call for heat - onlt the radiators in those two zones will heat up.
The valves I used were made by Honeywell, but I can't remember the part number now as it was such a long time ago.
The Roomstats I used were also made by Honeywell and were programmable so each zone could have its own independant on / off times.
Hope this helps.