Just a quick one, for those who have more experience and knowledge than I.
External gas meter, 22mm copper runs externally along wall around corner into kitchen also up the wall
and into landing for combi boiler. Water rises in kitchen in copper.
Question: Can you bond both services with one piece of 10mm earth cable, providing you do not break the cable at the first bonding clamp ? Do you bond the gas inside the kitchen even though it also runs outside
and up the wall ? or can you bond it in the meter cupboard and then run it along and into the kitchen for the water ? Please help, as I wish to finish as soon as possible and have a rest.
Many thanks, Pat
 
For a service pipe, the main bonding conductor should be connected as near as possible to the point where the service enters the building. The connection must be before any branched pipework and on the consumers side of any meter. If possible the connection should be made within 600mm of the meter outlet. Where the meter is outside, the bonding connection should be made at the point of entry of the service into the building. 544.1.2
Where a main bonding conductor loops in and out to connect to an extraneous-conductive-part, the conductor should be unbroken at the connection. 528.3.3

Hope this helps.
 
Good quote re regs there.

But I think the issue lies with th looney plumber / gas fitter.:rolleyes:

With the pipe outside the property, if you were to bond the gas in the kitchen that would be after the branch. Taking the cable outside and connecting to the pipe then means external influences on connection an bonding clip.

Although the 600mm cant be achived, because pipe outside and pipes inside after branch, I would connect in this case in meter box. Know this was done away with several Editions ago but think this might be best option.

Anyone any thoughts?:)
 

Reply to Bonding again in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
353
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
320
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
368

Similar threads

  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K
The power company only brings in 3 wires which is 2 live and 1 neutral wire. It’s our responsibility to add the ground rod to bond the neutral...
Replies
3
Views
593

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top