Hi guys any advice.
I have had a request for a consumer unit change. I always carry out a condition report prior to find any issues that need resolving. The installation has a few defects but no C1's . It's a TNS installation and the main earth is 10mm and bonding to gas and water both 6mm the gas is easy to upgrade to a 10mm but the water is another matter it's virtually impossible to get a new cable to the water stop tap without causing disruption to the internal fabric. The client wants no damage! And I don't have my magic wand.
So my question is it ok to leave the 6mm to the water, continuity has been confirmed and make a note on the installstion cert?
Thanks
 
This is what the regulation say. To mechanically protect single cord bonding conduction will not be economical. so 4mm2 will be cheaper. To use 6mm2 or above is only to satisfy ones unexplained psychology.
 
This is what the regulation say. To mechanically protect single cord bonding conduction will not be economical. so 4mm2 will be cheaper. To use 6mm2 or above is only to satisfy ones unexplained psychology.
Yep you just confirmed it.
 
Sorry Ian1981, mis-read your original post. You are correct the size should be 10mm2 as min. If you cannot pull new cable due to prior agreement with client not to damage any building fabric, and the exisiting cable is free from any damage including thermal, then I would put this down into the report and put C3 against it.
 
Hi guys any advice.
I have had a request for a consumer unit change. I always carry out a condition report prior to find any issues that need resolving. The installation has a few defects but no C1's . It's a TNS installation and the main earth is 10mm and bonding to gas and water both 6mm the gas is easy to upgrade to a 10mm but the water is another matter it's virtually impossible to get a new cable to the water stop tap without causing disruption to the internal fabric. The client wants no damage! And I don't have my magic wand.
So my question is it ok to leave the 6mm to the water, continuity has been confirmed and make a note on the installstion cert?
Thanks
For your installation the minimum size for the earthing conductor might be calculated to be in the region of 5mm² and therefore the size of the main bonding would be half this subject to a minimum of 6mm². You have 6mm², so it is fine and can be left as it is is with no consideration of non compliance.
 
For your installation the minimum size for the earthing conductor might be calculated to be in the region of 5mm² and therefore the size of the main bonding would be half this subject to a minimum of 6mm². You have 6mm², so it is fine and can be left as it is is with no consideration of non compliance.

Could you show your calculations Richard? :)
 
Hmm.
The adiabatic equation and the fact that the installation is TN-S suggest that the bonding conductors are correct and the installation Earth is oversized.
The Ze value of 0.11 ohms is very low and suggests that PME conditions apply, which would mean the bonding conductors are undersized and the installation Earth correct.
However, this is not a new installation, but an alteration to an existing one.
As such, the requirement is to ascertain whether the bonding and earthing is adequate for the protective measure intended to be used.
I imagine that ADS will be the protective mesure used, with additional RCD protection.
As neither require bonding to operate and the installation Earth complies, it would seem there is no requirement to upgrade either the earthing or bonding.
 
Regs are very clear on this, as Richard has already eluded to: TNS with a min earth of 5mm (as OP has calculated), bonding is half that to a min of 6mm. I wouldn't even install 10mm for the 'easy' gas, 6mm is fine and perfectly within the standard.
 

Reply to Bonding... can I keep it at 6mm? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top