were currently doing a job in massive old pub whats going to be a libary, my gaffer says put 10mm bonding to gas and water but how do you actually work out what size is required
just to add to this, i have just finished a apprentiship and i have never been taught about this, we do mainly houses so we allways install 10mm, but i just like to know for my own knoledge
just to add to this, i have just finished a apprentiship and i have never been taught about this, we do mainly houses so we allways install 10mm, but i just like to know for my own knoledge
lol
olo
lol
after thinking about what i said, we did get a breif lesson i remember the tutor saying bonding should be half size of the neutral, after just looking in regs it does say this but if you have any notes or links that would be great
why is it half the neutral though and not half x a phase presume sometimes the neutral is different sizes on 3 phase some time, i not had much experience on 3 phse
lol
olo
lol
Hi Chopper, another thing to watch is distance from MET; for example if you're up to 27/28 metres with your bonding 'run' then its at the limit of its required resistance ( <0.05 Ohms ). In this case (if it was,say,35 metres) then you should use 16mm2.
Is that right btw re: the 1/2 the neutral size just for TNCS? Isn't it for TN systems. Or am I wrong again!
Yes, a bit of confusion, it's sized in PROPORTION to the SUPPLIER'S neutral conductor (not the tails) on TN-C-S systems, and there isn't actually a 0.05 Ohm resistance limit on main protective bonding.