Hi Guys
Doing an EICR of a property.
The client has an outbuilding with gas and water supplies. It has it's own CU fed from the main CU in the house.
The water is bonded but the gas is not.
The water supply is underground from the house in plastic and then changes to copper which is bonded.

The gas supply comes from the house in an underground copper pipe linked to the gas pipes in the house. So, electrically, it would be subject to the bonding in the house.
But does this negate the need to bond it in the outbuilding?

Looking forward to wise words!

Cheers
Pete:confused:
 
Last edited by a moderator:
Why are you asking where equivalent conductance is mentioned when you go on to mention equivalent conductance yourself in you second paragraph.

I have no issue with their being other interpretations or however you wish to describe it. If you can provide links to the published documents/guidance which could be referenced if I did not follow the IETs guidance notes and I did have to defend my installation in court then I will consider using that guidance in my work.

Dave the first paragragh asks for the CSA to be half that of the Earthing conductor, so lets say the Earthing conductor need to be 20mm, would a 10mm steel Main protective bonding conductor be okay?

Cheers
 
Dave the first paragragh asks for the CSA to be half that of the Earthing conductor, so lets say the Earthing conductor need to be 20mm, would a 10mm steel Main protective bonding conductor be okay?

Cheers

If the required earthing conductor is 20mm steel and PME conditions do not apply then yes a 10mm steel main bond would be okay according to 544.1.1

But it would not comply if it is a seperate conductor (543.2.4)

And yes a main bond is included in the definition of a protective conductor (see definitions page.33)
 
If the required earthing conductor is 20mm steel and PME conditions do not apply then yes a 10mm steel main bond would be okay according to 544.1.1

But it would not comply if it is a seperate conductor (543.2.4)

And yes a main bond is included in the definition of a protective conductor (see definitions page.33)


Well no it wouldnt, a protective conductor 10mm or less needs to be copper 543.2.4.

Cheers
 
Dave could you explain this bit?

But it would not comply if it is a seperate conductor (543.2.4)

Cheers

A seperate conductor would be a conductor which does not form part of a cable or multicore cable and is not trunking, ducting, conduit. It's pretty clear if you read that regulation properly. It states that it only applies to the specified types of conductor referenced in parts of an above regulation.
 
A seperate conductor would be a conductor which does not form part of a cable or multicore cable and is not trunking, ducting, conduit. It's pretty clear if you read that regulation properly. It states that it only applies to the specified types of conductor referenced in parts of an above regulation.

Okay, so 543.2.4 takes us to 543.2.1 (i) to (v) agreed?

So how do you interpret 543.2.1, " A protective conductor may consist of one or more of the following"?

Cheers
 
Calculating the steel CSA required for a main bond is not the same as calculating the steel CSA required for a CPC. The requirement is that the steel CSA must give the same conductance as the required copper main bond. The calculation for working this out is given in guidance note 8 page 55, but it is basically the steel CSA must be greater than the product of the required copper CSA and the ratio of the resistivities of copper and steel.

The ratio of the resisitivities of copper and steel is given as 8.5, so the required minimum CSA of steel to be equivalent to a 10mm copper main bond is 8.5x10=85mm

That 6mm 4 core isn't looking so good really is it!
I was responding to the post that suggested using both the 6mm core and the SWA armour, which would mean the SWA would only require an equivilent conductance of 4mm copper.
I use the ratio of 1:9 when calculating.

Reference to copper equivalence is made in BS7671 when determining the CSA of bonding conductors where PME conditions apply.
 
Last edited by a moderator:
Okay, so 543.2.4 takes us to 543.2.1 (i) to (v) agreed?

So how do you interpret 543.2.1, " A protective conductor may consist of one or more of the following"?

Cheers

I interpret that as meaning a protective conductor could be made up of one or more of the listed items. So for example it could be that the sheath of an MI cable forms the protective conductor up to the point where the gland connects it to galv trunking which then also forms part of that protective conductor.

I think you are steering this in the direction of the earlier question as to whether it is acceptable to use 2 conductors of different materials and CSAs in parallel as a bonding conductor. And I concede that you could interpret this regulation as allowing it, but I whether or not that is the 'intent of the regulation' I don't know.
 
Hi Guys
It's the OP here! Fascinating and thought provoking discussion, not entirely clear.
FYI
1. The installation is PME
2. The SWA cable is XLPE 3 core, not 4.
3. I used a C3 with NICEIC Technical Support's blessing
4. My table gives the equivalent Cu size of the armour as 7.39 sqmm. Is that correct?
5. Under PME rules, I understand that the CPC should be 10mm. Is that correct?
6. As neither the core nor the wire armour are individually 10mm, is it your conclusion that they may be combined? If so, how do you calculate their combined Cu value?

Cheers
Pete
 
Hi Guys
It's the OP here! Fascinating and thought provoking discussion, not entirely clear.
FYI
1. The installation is PME
2. The SWA cable is XLPE 3 core, not 4.
3. I used a C3 with NICEIC Technical Support's blessing
4. My table gives the equivalent Cu size of the armour as 7.39 sqmm. Is that correct?
5. Under PME rules, I understand that the CPC should be 10mm. Is that correct?
6. As neither the core nor the wire armour are individually 10mm, is it your conclusion that they may be combined? If so, how do you calculate their combined Cu value?

Cheers
Pete

This is the argument that is raging lol, the regs say we cannot combine them, different materials ;), GN8 says not, they each have to comply in their own right, ie. 10mm ,or equivalent for the armourings.

This was partly my fault because I originally looked at a dodgy table which was over optimistic on the copper equivalent of the armourings. ;)

Geoff seems to think you can, lol

You can C3 anyway if the conductors are not showing any distress, degradation, thermal or otherwise and not less than 6mm.
 

Reply to Bonding Gas Supply in an Outbuilding in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I like your way of thinking.
Replies
6
Views
626
loz2754
L
Although the gas pipe may no longer require the bonding, it should really be terminated correctly or completely disconnected at the other end...
Replies
2
Views
452

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top