Hi I am recently qualified and still have a lot of learning/reading to do but Blue plastic waterpipe incoming, seems to always be a grey area with electricians I work with, me personally wouldn’t bond it..... Although we have to prove that in the plumbers install their is no copper going to earth?? Can someone enlighten me on this please

Many thanks..... and go easy on me lol
 
Carrying out a 500 v IR test from the MET to the piece of metal if you get 0.02 Mohms or higher then it’s believed not to be extraneous that is it won’t induce an earth potential if you follow the formula 230/ 0.01 amps= 23000 ohms.
Don't forget to factor in the average hunmanbody resistance of 1000 ohms deduct this from your calculated 23000 ohms gives 23000 minus 10000 = 22Kohms
 
So, we've (or I've learnt) two different tests or equations.

One for extraneous-conductive-parts as defined by reg 411.3.1.2 (equation suggested in GN8 6.1), and one for supplementary bonding, as defined by reg 415.2.2.

Sorted.
 
I’m interested into what Midwest has previously said about that change to the existing guidance on it.
Tho I suspect upgrading the bonding is more to do with New works carried out.
I’m aware that there’s no statutory law that requires that an electrical installation needs upgrading to the current regulations if you like but that new work must be designed and installed to the current edition of bs 7671.
What I was trying to say was that the certificate declaration says that you have not made the installation worse in terms of safety. If your work was compliant but the installation as a whole had problems then you would not have made things worse and so could complete the work without upgrading the bonding (for instance).

However this is countered by the requirement to ensure earthing and bonding is adequate for the protective measure employed.
Which takes precedence? Hmm open to interpretation.
Obviously the best thing to do would be to upgrade, but, as you say, it can be ridiculous to do so in some cases.
 
22 Mohms is the value which indicates a conductive -part is isolated from Earth (22Mohms if we take account of the resistance of the human body).
0.02 Mohms (20 Ohms) is the value which indicates a conductive-part is reliably connected to Earth and is the minimum resistance in the range which requires bonding.
7.67 kohms is the maximum resistance in the range which requires bonding (6.67 kohms if we take account of the resistance of the human body).
0.05 ohms is the maximum resistance for the connection of a bonding conductor to an extraneous conductive-part.
 
Yep your right pete. :)
22 Mohms is the value which indicates a conductive -part is isolated from Earth (22Mohms if we take account of the resistance of the human body).
0.02 Mohms (20 Ohms) is the value which indicates a conductive-part is reliably connected to Earth and is the minimum resistance in the range which requires bonding.
7.67 kohms is the maximum resistance in the range which requires bonding (6.67 kohms if we take account of the resistance of the human body).
0.05 ohms is the maximum resistance for the connection of a bonding conductor to an extraneous conductive-part.
7.67 would be if your using a 30mA rcd as your threshold if you like.
But 0.02 Mohms is not 20 ohms perhaps you misquoted?
0.05 ohms for a bonding conductor is only guidance at best as only GN3 references this value and not bs 7671 that is it’s not set in stone.
 
In reading GN8 6.1 again, it mentions the BS PD 6519, IEC 60479 Guide to effects of current on human beings & livestock, which apparently provides data for ZTL & IB.
For hand to hand contact, it gives a resistance of the human body of 1000ohms, and 0.5mA as the threshold of perception and 10mA as the let-go threshold.

Using those figures (specifically 10mA), gives a figure of 22kohms, suggesting the designer elects to accept the let-go threshold as a safe level. It also says the designer might need to consider variations in resistance & whether a lower limit on the current flowing threw the human body or livestock is necessary.

From that, can I deduce using 30mA as IB, resulting in a figure of 6.67kohms for RCP, is not recommended?

I do have a copy of a 'Connections Technical' that also gives a figure of 6.67kohms, from a calculation using a 30mA RCD. Makes you wonder who to believe!
 
It is up to the designer to decide what level of safety is required for the installation and so then specify the required level of resistance that is acceptable to determine the identification of extraneous conductive parts.
Generally 10mA is used because it is a catch all situation, not too bad not perfect.
If you have lots of large animals then less than 2mA may be the best approach, if there is minimal chance of any accidental contact and everyone in the area is adult then 30mA may be suitable.
 

Reply to Bonding gas/water yellow and blue in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
582
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
768
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
3K
  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top