Hi I am recently qualified and still have a lot of learning/reading to do but Blue plastic waterpipe incoming, seems to always be a grey area with electricians I work with, me personally wouldn’t bond it..... Although we have to prove that in the plumbers install their is no copper going to earth?? Can someone enlighten me on this please

Many thanks..... and go easy on me lol
 
It's not a grey area. If it's an extraneous conductive part it needs bonding. If it's not an extraneous conductive part it doesn't need bonding. I always run a green and yellow in for gas and water on a new builds as I've had muppet meter fitters refusing to connect as no bonding, even though it didn't require bonding. If they moan I connect it then chop it off when the muppet has finished.
 
Must admit, I'm still confusing myself over this. I understand the testing to conclude if a metal pipework after a plastic service is extraneous or not.

I take spinlondons point that bonding the above, under fault conditions may momentarily 'increase the number of conductive parts that will become live', but wouldn't these be earthed anyway by a circuit cpc?

The OSG recommends bonding of above, unless its been confirmed said pipework is not introducing Earth potential. It mentions pipework 'liable to introduce earth potential'. It doesn't mention testing to prove whether such pipes are extraneous, only gives examples, as in reg 411.3.1.2. Indeed the formulae for when doubt exists over effectiveness of extraneous or not, reg 415.2.2 is for supplementary bonding, something completely different. Reg 544.1.2 states where the consumers hard metal pipework should be bonded after insulating section or insert.

So I'm suggesting BS7671 recommends that unless you can physically confirm all such pipework is not liable to or not able to, then it should be bonded?
 
I don’t bother with the OSGs, as they contain so many errors.

Are you stating that the OSGs recommend bonding non-extraneous conductive-parts?

But it does contain some pretty pictures for us plebs. :)

Have a shufty yourself, it talks about it on pages 44 & 46 in the yellow version.
 
But it does contain some pretty pictures for us plebs. :)

Have a shufty yourself, it talks about it on pages 44 & 46 in the yellow version.
Unfortunately, that is not possible.
I only have a brown 16th and a red 17th someone gave me.
My point is however, BS7671 requires protective bonding for extraneous conductive-parts, not for non-extraneous conductive-parts.
 
Unfortunately, that is not possible.
I only have a brown 16th and a red 17th someone gave me.
My point is however, BS7671 requires protective bonding for extraneous conductive-parts, not for non-extraneous conductive-parts.

Oohh ok, give me 5 mins, I'll type up what the OSG says. Might be 10, just sipping a G&T :)
 
Yellow OSG Sec 4.5 'Main protective bonding of plastic services'. There's no shock here (excuse the pun), it says there's no requirement to bond plastic services.

Continuing on page 46; 'Where there is a plastic service and a metal installation within the premises, main bonding is recommended unless it has been confirmed that any metallic pipework within the building is not introducing Earth potential (see 4.3, (referencing to reg 411.3.1.2).

I have had a quick shufty through GN8, and can't seem to find specific mention of the above scenario.

What do you make of the definition of extraneous-conductive-part in BS7671?
 
Yellow OSG Sec 4.5 'Main protective bonding of plastic services'. There's no shock here (excuse the pun), it says there's no requirement to bond plastic services.

Continuing on page 46; 'Where there is a plastic service and a metal installation within the premises, main bonding is recommended unless it has been confirmed that any metallic pipework within the building is not introducing Earth potential (see 4.3, (referencing to reg 411.3.1.2).

I have had a quick shufty through GN8, and can't seem to find specific mention of the above scenario.

What do you make of the definition of extraneous-conductive-part in BS7671?
That was 16mins :eek::p
 
NHBC “snagged” me on this on some new builds, yellow plastic incoming on the gas with about a meter of copper on show ran inside a garage clearly not extraneous and tested to prove so. Even after exerts sent from regs/osg apparently it wasn’t acceptable and they wouldn’t issue their cert or warranty. I was very annoyed as I had to go back and bond all of them which cost me money and made me look like I was in the wrong. He said “everyone else runs an earth to it so you are clearly in the wrong” could of smacked the smug ---.
 

Reply to Bonding gas/water yellow and blue in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
519
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
754
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
3K
  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top