Hi guys,
Basically I went to look at a job one of my electricians is doing in a flat above a restaurant.
New supply from the DNO into communal hall which leads solely to the flat.
He has put a main DB there, and from this is a sub to flat, lighting, lift and cleaners socket.

There is no pipe work in this area at all and gas and water service enter in the flat.

I just wanted a 2nd opinion on these being bonded to the flat db and not the MET??

Flat board is fed on a 10mm 3core swa.

Thanks in advance, it's been a long week lol
 
The Flat CU/DB earth bar will in effect be the EMT that will be connected to the MET. So it's fine to run all of the flats bonding cables to the EMT!!
 
Thanks E54! that was my thinking. Obviously if there was pipework there i tell them to bond it to the MET in the normal set up.

Also on the certificate they have left the Main protective bonding conductors section blank....

Im right in saying that it should be filled out no matter if it is bonded to the MET or a sub board?
 
Also on the certificate they have left the Main protective bonding conductors section blank....

Im right in saying that it should be filled out no matter if it is bonded to the MET or a sub board?

Yes, you're correct.

In an ideal world they would be connected to a MET at the origin and individually marked for future identification but there's nothing wrong with connecting them to the earthing terminal in the Flat DB as the CPC to the Flat DB is suitably sized at 10mm2.
 

Reply to Bonding in communal hall. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
185
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

You would have to say internal.
Replies
5
Views
338
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top