Hi all
Wondered if you could clear up a debate we are having at work.
Gas inspection has said no bonding to the gas meter or pipe in block of flats.

One engineer says it should be run to the meter.
One says it should be installed outside within 600mm of where it enters the building on the blue arrow.
And one engineer says it should be inside 600mm from where it enters the flat.
What do you all think.
1000032584.jpg
 
BS7671 states, where practical the connection shall be made within 600mm of the meter outlet union or at the point of entry to the building if the meter is external.
So, I would suggest your last engineer is correct.
 
DNO policy document for multi way distribution systems (Ryefields) requires bond at the incomer plus a bond in each individual flat
 
BS7671 states, where practical the connection shall be made within 600mm of the meter outlet union or at the point of entry to the building if the meter is external.
So, I would suggest your last engineer is correct.
You would have to say internal.
 

Reply to the thread, titled "Clear up a bonding debate of ours." which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Thread starter

Joined
Location
Cm234pl
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Clear up a bonding debate of ours.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5

Thread statistics

Created
Robb04001,
Last reply from
westward10,
Replies
5
Views
385
Back
Top