... but if there is no continuity between t'pipe in t'ground and t'pipe entering t'house then the cast iron is not an extraneous part!
I’ve just looked in the 16[SUP]th[/SUP] OSG. Bonding a metal soil pipe in a bathroom was a requirement.
I’m going to make a wild guess being as the OP has cleared off, he’s found a bonded pipe doing an inspection and it’s not in his IET comic book.
First i isolated the installation, then using an insulation resistance tester, connect one lead to the main earth terminal and the other lead to the soil pipe, tested at 500v and my reading was much less than 23,000 ohms meaning that the soil pipe is considered an extraneous conductive part and needs main bonding
First i isolated the installation, then using an insulation resistance tester, connect one lead to the main earth terminal and the other lead to the soil pipe, tested at 500v and my reading was much less than 23,000 ohms meaning that the soil pipe is considered an extraneous conductive part and needs main bonding