HI all,
just need clarification on bonding of a mains cupboard please.
Setup is
Mains cupboard 2mtrs wide and 6mtrs long
10 cutouts feeding 10 flats , has meters then tails to cutout then 25mm concentric to each flat
5 water tanks are in there and cables from flats feed the immersion heaters, cooper pipes from tanks then above ceiling all plastic, also plastic feed coming in.
lighting and power in main cupboard off 5x5 split board all rcd, with PV inverter, and aerial boosters.
company has come in and said all the cooper needs bonding, its all plastered now so I think they might be assuming that all the installation is in copper but its not, I haven't bonded as I usually don't need to , but think that the cupboard is so narrow you can touch the cutouts (non RCD) and the copper of the water tanks, just need some guidance please .
Cheers
Grand
just need clarification on bonding of a mains cupboard please.
Setup is
Mains cupboard 2mtrs wide and 6mtrs long
10 cutouts feeding 10 flats , has meters then tails to cutout then 25mm concentric to each flat
5 water tanks are in there and cables from flats feed the immersion heaters, cooper pipes from tanks then above ceiling all plastic, also plastic feed coming in.
lighting and power in main cupboard off 5x5 split board all rcd, with PV inverter, and aerial boosters.
company has come in and said all the cooper needs bonding, its all plastered now so I think they might be assuming that all the installation is in copper but its not, I haven't bonded as I usually don't need to , but think that the cupboard is so narrow you can touch the cutouts (non RCD) and the copper of the water tanks, just need some guidance please .