Do you think these steel stantions require to be main bonded [ElectriciansForums.net] Bonding on a farm
 

Attachments

  • [ElectriciansForums.net] Bonding on a farm
    2011-11-30 15.38.44.jpg
    109.4 KB · Views: 31
  • [ElectriciansForums.net] Bonding on a farm
    2011-11-30 15.38.56.jpg
    66.7 KB · Views: 46
  • [ElectriciansForums.net] Bonding on a farm
    2011-11-30 15.39.11.jpg
    109 KB · Views: 36
Test between the steel and the MET. If you get less than 22kohms, then it needs bonding. To be honest, those stantions will if bonded help to bring down your Zs, due to the concrete that will have a large surface area that will be in contact with earth.
 
Additionally to the normal main bonding of structural steelwork within the barn, if the stanchions and any other extraneous-conductive-parts or exposed-conductive-parts can be touched by livestock they MUST all be supplementary bonded in accordance with BRB 705.415.2.1
 
Last edited by a moderator:
The structural steelwork of this building does need to be bonded the the buildings MET/EMT. However the steelwork is already interconnected by the cross beams etc, so pointless trying to supplementary bond them.

If this is a TT supplied building, the steelwork will in all honesty have a better Ra value than the usual 1 metre rods used. The only thing i might consider doing, is to drive a deep driven rod and connect that to the steelwork. That will certainly stabilise the earthing to this structure if the concrete base is a flimsy affair that's often associated to farm building structures...
 
Cheers guys
It a tns system and there are about ten of these all seperated from the main steelwork which ia not bonded either. I will be back sometime this week so will test it then.

Thanks
 

Reply to Bonding on a farm in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
775
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
783

Similar threads

I understand your question and it can be a can of worms, on the one hand as mentioned in your previous reply is it a extraneous conductive part...
Replies
2
Views
690
  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top