G

graham123

am currently doing a pir on a secondary school, in the toilets their is no cross bonding under sinks. Is this a code 2, or 4?. The DB which covers that area has no RCD protection for any circuits
 
am currently doing a pir on a secondary school, in the toilets their is no cross bonding under sinks. Is this a code 2, or 4?. The DB which covers that area has no RCD protection for any circuits

There is no requirement for 'cross bonding' in toilets and the circuits only need RCD protection if they are buried in walls at depths of less than 50mm without earthed metallic sheaths/protection.

Graham, you've done the right thing asking the question but you really should know this stuff if you're doing periodic inspections-do you have a copy of BS7671:2008?
 
probably been talking to a gas fitter who thinks that everything metal should be bonded. i've even seen bonding from a cistern feed to it's outlet in a gents at a social club. turns out one of the committee is a retired spark whose last job was 15th edition.
 
but it does no harm, just a waste of cable....?

It's not so much that some unnecessary cable and clamps are used but the fact that the inspection/testing should be carried out by a competent person with an above-average knowledge of BS 7671:2008.

Bonding requirements are a very important part of a periodic inspection and should be second nature to a competent inspector.
 

Reply to bonding, pir school in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K
  • Question
Surely one of the most important parts of supplementary bonding is to bond the radiator and hot tap/pipe to the cold one. Both the hot tap and...
Replies
32
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top