So I know why it is done, where it is done and how it’s done, but I’m yet to see a scenario where there is shock danger in a typical bathroom in a dwelling provided a) the main bonding is in place and b) the CPC’s of all circuits are connected together in the CU (as they will be).
Consensus is on an EICR code 2 where there is no RCD for additional protection and supplementary bonding is not in place. What is the potential danger ? What am I missing ?
I meant to cover that, in this case answer is no. Shower feed is plastic through the back, the only thing that came close was the bath taps but I checked and that has plastic plumbing too. Sink has a copper cold pipe but is completely out of reach (and also behind the pedestal)
C3 for the lack of sup bonding. I think this is suggested in BPG4, but check that.
C2 for the no RCD for the shower, but that is my personal opinion.
Sorry, Shower is on the RCD side of the board. Just lights and immersion are not.
So regs issues are ack of RCD for domestic lighting, and lack of supplementary bonding as not every circuit in room has RCD protection.
It's a proteus board so a couple of RCBO's wouldn't be a bad plan if I can sell the concept.
I take your point and many would do that. I have a working relationship with this letting agency that minor things I 'just fix'. A real bug bear of mine is an unsatisfactory EICR because there's a sticker missing on the consumer unit! I honestly think it works better for everyone to just resolve things that are easily resolvable.
I know where you’re coming from with that but unless it’s a code 2 then I’m on an issue is not going to result in an unsatisfactory EICR and if indeed you remedy issues on the fly they won’t be reported against as being an observation on the report anyway.
The whole code 2 versus code 3 area is indeed very grey. All electrical equipment is potentially dangerous by its nature. I think it should be code 1: as is, immediate danger - requires isolation/locking off, code 2: improvements REQUIRED to improve safety (e.g add RCD protection, single insulation visible, damaged accessories, ) 3: improvements RECOMMENDED to improve safety or to comply with current regs, e.g add SPD, add AFDD, replace Type AC with type A, replace plastic CU under stairs etc
I’ve taken the view on rental properties to err on side of code 2 versus code 3 on the basis that there is an increased likelihood from tenants misusing , damaging or disrespecting equipment and / or not reporting or paying to have it fixed having done so. Basically I’m taking into context the environment of the installation as well as the technical elements and its age. Landlords have a duty of care to ensure the safety for their tenants and if that means upgrading or replacing a consumer unit that does not have RCD protection even though that may technically fit within code 3 world . After all for say £600 quid or a CU swap with SPD and RCBO’s is that not a good investment for the next 20 years ? It would be replacing something that is really beyond its serviceable life in any case
My take on supplementary bonding:
I don't think it's intended as a backup CPC, although it can achieve that. Its full name "supplementary protective equipotential bonding", and that it includes extraneous parts, leads me to conclude that its main goal is equal potential. The formula we need to meet is:
R <= 50V/Ia (Ia= operating current of protective device)
When a fault to earth occurs, a circuit is completed through which a current flows. As long as this current flows, there will be a voltage drop between the site of the fault and the MET, so there will be a potential difference between the site of the fault, and all metalwork connected to the MET. The aim of supplementary bonding, as I understand it, it to keep that potential difference to no more than 50V.
Example: electric shower without RCD protection, on a B40. Extraneous pipework in touching distance, connected to the MET via main bonding.
Fault of negligible impedance occurs at shower, 200A flows. There is a voltage drop between the shower and the MET, and therefore a potential difference between the shower and the nearby pipework.
50/200 = 0.25ohms
As long as the resistance between the shower and the pipework is 0.25 ohms or less, then the voltage between them will be no more than 50V.
The above example is for a fault that caused instantaneous disconnection. Supposing a tenuous fault occurred that didn't cause instantaneous disconnection. Let's use a fault current of 199 ohms, as this is right on the edge:
50/199 = 0.251 ohms
So as the fault current gets lower, the max resistance between the shower and pipework to keep the potential down to 50V gets higher. If you meet the formula in 415.2.2, then any fault will either instantly disconnect, or will be kept to 50V or lower.
50/200 = 0.25ohms
50/199 = 0.251 ohms
The 50V rule makes sense. In any case a fault current (not overload) will take out the OCPD in 0.4s provided max Zs has been met. So either a short or Ipf of 200ohm and the OPCD surrenders instantly or you’ve got up to 0.4 seconds of pain between 50V and 240V on a linear scale with reference to the resistance between the extraneous conductive part to the MET and the fault current ?
I think the point of sup bonding is when a fault occurs that doesn't produce enough current to operate the device in the required time, so the victim could be subjected to a voltage for longer than 0.4 seconds. I assume that the sorts of faults that it deals with are considered tolerable in general, but not in the high-risk situations that SB is required (eg bathrooms).
I suppose this would be faults where there is not a direct metal-to-metal short. Perhaps a heating element that has corroded and is connecting to earth through moisture may be of higher impedance, may take some time to disconnect. Or perhaps if there was a problem with low supply voltage.
@Pretty Mouth thanks for taking the time to write a textbook answer with good examples.
With so many installations having Dual RCD boards or RCBO boards it's scary how easy it is to forget the details of regs that don't need to be regularly considered day in and day out.
You're welcome. I found that it isn't very well explained in the textbooks that I have read, plus it is difficult to get the head around anyway, which may be why many of us aren't 100% on it.
I’m still not convinced that with the parallel paths of the ECP and CPCin a dwelling there would be any significant PD 😆 take a standard 3bed semi with the CU under the stairs , this is no further than the loft or airing cupboard In practice from the bathroom in many cases
Must be a very low ceiling to code it for not being ip rated :)
It is, and I'm not exactly short of reasons to condemn this light!