I know this has probably been discussed to death, but..........

I looked at a job to provide electrics for a loft conversion. Part P required as Building control are involved. No issues there.

However i stated that the water and gas require bonding back to CU in 10mm. The customer had a new boiler fitted in the loft by British Gas and the Elecsa spark that wired the boiler controls bonded the gas and water supply at the boiler, back to the CU in 6mm, claiming that is acceptable under the 17th edition, as an RCD is fitted, and bonding is not now required.

Please verify that i'm not missing something.
 
Eh?? Main bonding is always required, it is how ADS works....it is the cornerstone of safe electrics! Are you saying that the water and gas is bonded together in the loft then run back to the CU elsewhere? If so, that's totally WRONG! As you know....
 
what i'm more concerned with is that an Elecsa registered sparky (i'm also Elecsa), contracted by British gas, is convincing customers that what he has done is correct.

I'm also getting the feeling that the customer may be feeding me some of the brown stuff. As a week or so ago, i had a call from a woman, requesting that i test the electrics that her husband had fitted in their loft conversion, so that they could get a CofC from building control. I said no thankyou, she didn't seem phased by my answer, as if i wasn't the first person to turn her down.
The guy has boarded the loft out and fitted insulation etc without running cables, although he has left certain parts unfinished. I think he may have ripped the cabling out, to make it look as if he hadn't done it, and his interpretation of the bonding is what is currently there.
He does have some understanding of the regs, but i think it is more what he has been told, rather than what he knows.
 

Reply to Bonding services. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
841

Similar threads

  • Question
Thank you, that's a really helpful post, nice & clearly stated and helps me clear up a lot of confusion on this matter.
2 3 4 5
Replies
65
Views
6K
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
981

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top