I have never stated dp rcbo's MUST be used where an upfront rcd is in service, if you read back through my posts I clearly agree other options are compliant such as a dual rcd board.
What I do state (very clearly I believe) and stand by is that wherre rcbo's ARE used......they must be dp where there is a upstream s type rcd and in that arrangement are effectively a requirement, you seem incapable of understanding that I am only refering to where rcbo's ARE used. I believe i have been quite clear that with other arrangements sp rcbo's are compliant.
Perhaps you would be good enough Mainline to answer this.

Lets say you have a job where the designer has specified DB's with rcbo protection to all final circuits. A main switch of s type rcd is also specified. Its a TT earthing system.
Would you install sp rcbo's and provide an EIC on completion?
You said There is no specific regulation stating that a dp protective device is required for a tt with an upstream s type rcd.

Which was my point from the start.
That it’s Not a requirement.

@westward posted the same statement as I was typing saying dp rcbos aren’t a requirement and your reply was yes they are and proceeded to try and find a situation where they would be an actual requirement which has now come down to a designer telling you to fit them 🤣🤣

You can go through all the scenarios you like where the use of them is going to be the sensible thing to do but That would still not make it a requirement.


If a main switch rcd is within the enclosure I would be questioning the competence of the designer
 
Last edited:
I work a lot on a rural converted estate with 21 holiday cottages which were wired by the owner over the last 40 yrs tails running 20 Mtrs through 3ft thick walls and attics.

Added over the yrs is wind/solar and now comes the batteries and more solar along with ev points and bore hole pumps.
There is a mixture of Pme/tt along with stables swimming pools and spas.

To have an upfront rcd for no other reason but to be a backup wouldn’t be very sensible especially in the above situation.

I do everything i can do to avoid the use of them.
 
You said There is no specific regulation stating that a dp protective device is required for a tt with an upstream s type rcd.

Which was my point from the start.
That it’s Not a requirement.

@westward posted the same statement as I was typing saying dp rcbos aren’t a requirement and your reply was yes they are and proceeded to try and find a situation where they would be an actual requirement which has now come down to a designer telling you to fit them 🤣🤣

You can go through all the scenarios you like where the use of them is going to be the sensible thing to do but That would still not make it a requirement.


If a main switch rcd is within the enclosure I would be questioning the competence of the designer
Unfortunately you have chosen to ignore the fact that I am only referring to a situation where an up front s type rcd is used with rcbo final circuit protection, a common arrangement but not the only one. In that case sp rcbo's are not compliant. At no point have i suggested other compliant arrangements are not possible.
Clearly you have not answered my question because you know you cant without admitting that for the specified arrangement sp rcbo's not compliant.
 
Unfortunately you have chosen to ignore the fact that I am only referring to a situation where an up front s type rcd is used with rcbo final circuit protection, a common arrangement but not the only one. In that case sp rcbo's are not compliant. At no point have i suggested other compliant arrangements are not possible.
Clearly you have not answered my question because you know you cant without admitting that for the specified arrangement sp rcbo's not compliant.
why would I say that they were compliant when they are not ?

Dp rcbos would do the job but that doesn’t mean it’s a requirement and that’s what you have to fit. You said yourself that there is No specific requirement to fit them.

If you believe there is a requirement to fit dp rcbos on upfront rcds then carry on.
 
Just a follow up on the original questions I posted.

The 10 way main CU (all MCBs) has this.....

1) one dedicated MCB for the back garden where there is a small CU that feeds a garden lights, outside socket and a car charger. This external CU has all RCDs.
2) one MCB for the lounge sockets. This has a fused spur in the lounge that then feeds a single outdoor CU to the front and has an a single RCD.

Photos of the outdoor CUs attached.

The question is, if I get the main CU replaced with 10 RCBOs gather this will impact the outdoor RCDs?

Or can I have an RCBO and RCD on the same circuit?

For the back garden (1 above), it has a dedicated circuit on the main CU so we could just have an MCB rather then a RCBO on the main CU?

For the front garden (2 above), would it be wise to have an RCBO at the main CU, but replace the outdoor old RCD with a MCB?

Appreciate any thoughts.

It's never straightforward!!!
 

Attachments

  • IMG_1732[1].JPG
    353 KB · Views: 17
  • IMG_1595.JPG
    399.1 KB · Views: 12
One more....

My gas mains is earth bonded with a 10mm cable, this is near the CU (understairs cupboard).

Can the water (hot/cold) and heating flow pipes be cross bonded (interlinked). This cross bonding would happen under the comobi boiler with is not near the CU.
 
The question is, if I get the main CU replaced with 10 RCBOs gather this will impact the outdoor RCDs?

Or can I have an RCBO and RCD on the same circuit?
You can but it is not good design practice. It also depends on the cable between the CU and the outdoor blocks:
  • If that cable needs additional RCD protection then you need RCD/RCBO at the CU.
  • However, if it is something like SWA, adequately glanded to earth the armour and with a low enough end of circuit Zs to disconnect on a MCB alone, then you would be best to have just the remote RCD and feed from a MCB.
MCB feeding MCB+RCD or RCBO is still not ideal as selectivity on high faults is rather poor, but slightly less troublesome than upstream 30mA RCD and acceptable for non-critical areas like a shed, etc.

If loss of lights from the common upstream MCB/RCBO presents a hazard then you need to look at feeding off a suitable switched-fuse for better selectivity, or better still install emergency lights (i.e. internal battery sort) so they come on when power fails due to any reason.
 
Thanks.

I'm thinking....
1) replace the Protek RCB for a MCB.....
2) replace the GE RCD switch for a non-RCD one....

Then get an electrician to put in RCBOs on all circuits on the main CU.

I'd hate to spend all the money on a new CU and end up with the odd MCB within it.
 

Attachments

  • IMG_1595.JPG
    399.1 KB · Views: 6
  • IMG_1732.JPG
    353 KB · Views: 19
One more....

My gas mains is earth bonded with a 10mm cable, this is near the CU (understairs cupboard).

Can the water (hot/cold) and heating flow pipes be cross bonded (interlinked). This cross bonding would happen under the comobi boiler with is not near the CU.
No cross bonding required if rcd protected.
 
Why?

If that is the best overall design option then you should accept that.

If it is better to have RCBO at the CU and replace ageing RCD at the outdoor locations then fine, but that is not an argument for/against MCB at the CU as such.
Thanks for the feedback.

My comment was related to a point made earlier....by going the MCB route there would be no RCD protection on the cable between the indoor and outdoor CU. It's probably at least 10m long and just a normal cable - not SWA.
 
Thanks for the feedback.

My comment was related to a point made earlier....by going the MCB route there would be no RCD protection on the cable between the indoor and outdoor CU. It's probably at least 10m long and just a normal cable - not SWA.

What type of cable is it and how is it installed?

Does it need RCD protection and would it actually be achieving anything if it was provided?
 
Just seems like a standard cable out of the CU, chunkier then the others.

Not sure how it gets outside, possibly behind the kitchen units.
 

Attachments

  • IMG_1733.jpeg
    526.6 KB · Views: 16
Just seems like a standard cable out of the CU, chunkier then the others.

Not sure how it gets outside, possibly behind the kitchen units.
If you are not certain it is safe from DIY nailing, etc (i.e. if it could be hidden less then 50mm from the surface of a wall/flooring/etc) then it will need RCD protection. Here your best choice is an RCBO at the CU and then whatever at the out buildings.

Leaving the existing RCD there is not a big deal, not ideal perhaps, but not such an issue as worth a lot of work to change it unless you are making changes anyway.
 
If you are not certain it is safe from DIY nailing, etc (i.e. if it could be hidden less then 50mm from the surface of a wall/flooring/etc) then it will need RCD protection. Here your best choice is an RCBO at the CU and then whatever at the out buildings.

Leaving the existing RCD there is not a big deal, not ideal perhaps, but not such an issue as worth a lot of work to change it unless you are making changes anyway.
Thank you, that's a really helpful post, nice & clearly stated and helps me clear up a lot of confusion on this matter.
 

Reply to After a New Consumer Unit, now I need EICR & 100A DP Isolation Switch in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
909
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
42
Views
2K
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
5K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock