B

bobsteroo

i have been working with this electrician giving him a hand we have had a disagreement
about bonding
the main building has a 3 phase tns supply from there a 16mm 4 core swa and seperate 16mm earth goes to a brick built building a new extension has just been constructed
with 6 seperate steel stanchions or girders which or not connected with steel purlins or similar i say you should take a seperate earth back to the main dis-board in existing building
and run an earth between girders he says he will put an earth rod by 1 of the girders and run an earth between girders can any one settle this thanks:confused:
 
nope you are correct its structual steel and should be treated as water gas etc and bonded back to the board ,
 
Last edited by a moderator:
i have been working with this electrician giving him a hand we have had a disagreement
about bonding
the main building has a 3 phase tns supply from there a 16mm 4 core swa and seperate 16mm earth goes to a brick built building a new extension has just been constructed
with 6 seperate steel stanchions or girders which or not connected with steel purlins or similar i say you should take a seperate earth back to the main dis-board in existing building
and run an earth between girders he says he will put an earth rod by 1 of the girders and run an earth between girders can any one settle this thanks:confused:

That will just make things worse, IMO, they will definitely be introducing earth potential into the building.

I assume you are installing a CU and earth bar in this new building.

The steel stantions need only be bonded to this and the 16mm CPC will act as both earthing & bonding conductor.

The earth bar in the new building is termed an EMT (Earth Marshalling Terminal), and can be treated as a remote MET - all earthing and bonding can be run to this. (This is so long as the CPC of the feed to the building is of sufficient size to act as a bonding conductor as well)
 

Reply to bonding steel girders [stanchions] in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
813

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top