Cabinet was all metal construction bolted together, with 4 earth connections in each corner of the cabinet and on wheels
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Bonding to Data Cabintet in the Commercial Electrical Advice area at ElectriciansForums.net
perhaps we should use the term connecting it to earth as we would an exposed conductive part (not convinced that a cabinet is this)rather than the term supplementary bonding.Just trying to understand
The supplementary bonding conductors link the extraneous conductive, exposed conductive parts and cpc in the room with the aim to establish an equipotential zone and reduce touch voltages during a fault. I'm not sure what the other parts are that will be linked by the proposed 4mm? (there's just a rack). Given the steel framed wall RCD to be used so any fault cleared pdq?
I have done this for a data company who specified a 4mm supplementary bond to the metal cabinet.
There's maybe an argument of is it really a requirement but they insisted.
I supplementary bonded it from the supply circuit that fed the cabinet
How did you earth the detachable side panels, if it had any.
No!Rather strange, the avatar you two chaps (# 14 &15) use, are strikingly similar. You seem to argue a lot, are you actually the same person with a bipolar disorder
I am in disguise, not sure what Ian's excuse isRather strange, the avatar you two chaps (# 14 &15) use, are strikingly similar. You seem to argue a lot, are you actually the same person with a bipolar disorder
This may be something to do with other telecommunications standards (BS 6701, BS EN 50174-1, BS EN50174-2).
I haven't seen these standards myself, but have seen them mentioned in various places.