No 2 cabes not okay by the current regs.
The protective bonding cable has got to be continuous no breaks at all.
Sorry, that’s nonsense. Either individual conductors to gas and water, or one single, continuous conductor serving both.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Bonding to Gas and water am2 in the The Welcome Forum area at ElectriciansForums.net
No 2 cabes not okay by the current regs.
The protective bonding cable has got to be continuous no breaks at all.
No 2 cabes not okay by the current regs.
The protective bonding cable has got to be continuous no breaks at all.
No 2 cabes not okay by the current regs.
The protective bonding cable has got to be continuous no breaks at all.
Sizing main protective bonding conductors - https://www.voltimum.co.uk/articles/sizing-main-protective-bonding-conductorsSorry, that’s nonsense. Either individual conductors to gas and water, or one single, continuous conductor serving both.
Section 54Can you quote the regulation number stating this please?
For the record I prefer an unbroken cable if I was only using one
It is not nonsense, protective conductors have got to be continuous.Sorry, that’s nonsense. Either individual conductors to gas and water, or one single, continuous conductor serving both.
Guidance note 8 (earthing & bonding) page 57.
Thanks not got GN 8 does it say anything about seperate conductors being no compliant? because I think the post saying it is, and a single conductor is the best practice is incorrect.Section 54
It is not nonsense, protective conductors have got to be continuous.
It is up to you if you want to use one conductor for water and another conductor for gas but continuity is key no breaks at all.
Guidance note 8 (earthing & bonding) page 57.
Thanks not got GN 8 does it say anything about separate conductors being no compliant? because I think the post saying it is, and a single conductor is the best practice is incorrect.
Hit, nail and head and rather proves my point I think.
I would have thought that you would have it Pete!
Thanks Telthere is no reg. stating that a single bonding conductor to 2 services should be continuous. it's just been accepted as good practice for the reason i stated in post #5.
You can argue as much as you want and dismiss advice here.Right - this isn't a reg, its guidance
Most people don't have the Guidance Notes ......
If the IET intended this to be a reg it would be in the big book