Ok, I'm fresh and free of inebriation so hopefully I can make crystal clear my stance on supplementary bonding in a location containing a bath or shower. Here goes:
Local supplementary equipotential bonding according to Regulation 415.2 shall be established connecting together the terminals of the protective conductor of each circuit supplying Class I and Class II equipment to the accessible extraneous conductive parts, within a room containing a bath or shower.
Where the location containing a bath or shower is in a building with a protective equipotential bonding system in accordance with Regulation 411.3.1.2, supplementary bonding may be omitted where all of the following conditions are met:
1. All final circuits of the location comply with the requirements for automatic disconnection according to Regulation 411.3.2
2. All final circuits of the location have additional protection by means of an RCD in accordance with Regulation 701.411.3.3
3. All extraneous conductive parts of the location are effectively connected to the protective equipotential bonding according to Regulation 411.3.1.2.
The effectiveness of the connection of extraneous conductive parts in the location to the main earthing terminal may be assessed, where necessary, by the application of Regulation 415.2.2 (R≤50V/I[SUB]a[/SUB]).
When carrying out an EICR, upon entering a bathroom the first test to be carried out is one to establish whether or not there are any extraneous conductive parts within the location. The result measured between any metallic pipework and/or structural metalwork and the main earthing terminal should be above 45kΩ (some are happy using the figure of 22kΩ) to establish that the part is not extraneous. If any metallic pipework and/or structural metalwork is found not to be extraneous then it does not require bonding of any kind. If you have established that there are extraneous conductive parts, the next set of tests are between each extraneous and between each exposed conductive part to the main earthing terminal. The value you are aiming for to determine an effective connection between the main earthing terminal and an extraneous conductive part is around 0.05Ω, this does not take into account any length between the main equipotential bonding connection and the place upon that extraneous conductive part where you are carrying out the test. A 10mm bonding conductor will be within 0.05Ω up to 27m (it is reasonable within an average sized property to get a reading within 0.05Ω from the point of testing back to the main earthing terminal as copper pipe has a larger csa than that of a 10mm conductor). From the point at which you test an extraneous conductive part back to the main earthing terminal you will establish an effective connection to earth by the application of R≤50V/I[SUB]a[/SUB] where I[SUB]a[/SUB] is the operating current of the highest rated protective device serving a circuit within the location. This also applies to any exposed conductive part.
If the resistance between each point tested and the MET is less than or equal to 50V/Ia then each point is effectively connected to earth. For the purpose of this discussion I shall assume that in every case all final circuits of the location comply with the requirements for automatic disconnection. If the circuits within the location have 30mA RCD protection then no supplementary bonding is needed.
If all circuits within the location do not have 30mA RCD protection then a test between each simultaneously accessible exposed and extraneous conductive part should be carried out. The resulting resistance between any two simultaneously accessible exposed or extraneous conductive parts should be equal to or less than 50V/I[SUB]a[/SUB] (which given the measurements taken which have already ascertained that each part is effectively connected to the main earthing terminal using this equation, is highly likely). If the results are within this value, then it can be assumed that supplementary bonding is in place and this particular section of the installation be given a C3 as a 30mA RCD should be recommended.
Now, if the resistance between one or more exposed and/or extraneous conductive parts tested and the main earthing terminal is greater than 50V/I[SUB]a[/SUB] then an effective connection between those parts to earth has not been established (it is easily possible to have an extraneous conductive part that is connected to the main equipotential bonding but just not effectively [say for example 100Ω is measured between a radiator and the MET and plastic pipe feeding the radiator is visible]). We now know that this part should be supplementary bonded because it is extraneous but not effectively connected to earth. A test between this part and all other simultaneously accessible exposed and extraneous conductive parts can be carried out to ascertain whether or not supplementary bonding is already in place by applying R≤50V/I[SUB]a[/SUB] (although at the same time as carrying out this test we can safely assume it is not).
Regardless of whether or not all circuits in the location are protected by a 30mA RCD, this particular section of the installation must be given a C2 because of the lack of required supplementary bonding. Remember, supplementary bonding can only be omitted when all three of the above listed conditions are met.
If the bathroom does have 30mA RCD protection then this in particular warrants no code even though the lack of required supplementary bonding to a non-effectively connected extraneous conductive part has already been given and still warrants a C2. If the bathroom does not have 30mA RCD protection then as stated in one of the previous paragraphs, a C3 must be given (additional protection by way of a 30mA RCD is recommended). This again is in addition to the C2 for lack of required supplementary bonding. Addition of a 30mA RCD covering all circuits in this location will make no difference to the C2 that must be given for lack of required supplementary bonding.
I feel I must make this point absolutely clear: During testing and inspection or installation, if within a location containing a bath or a shower an exposed and/or extraneous conductive part is not effectively connected to earth (see above on how to determine an effective connection) then the existence/addition of a 30mA RCD does not absolve the inspector/installer of any responsibility to code the lack of supplementary bonding/install supplementary bonding to that part!!!
This is, always has been and always will be my stance on supplementary bonding within a location containing a bath or shower. This is as written in black and white in BS 7671 and I will not bend, break nor falter from this stance unless someone can prove beyond all doubt that my stance and that of BS 7671 is completely, utterly and totally wrong!
Now, time for a beer... or ten!
Local supplementary equipotential bonding according to Regulation 415.2 shall be established connecting together the terminals of the protective conductor of each circuit supplying Class I and Class II equipment to the accessible extraneous conductive parts, within a room containing a bath or shower.
Where the location containing a bath or shower is in a building with a protective equipotential bonding system in accordance with Regulation 411.3.1.2, supplementary bonding may be omitted where all of the following conditions are met:
1. All final circuits of the location comply with the requirements for automatic disconnection according to Regulation 411.3.2
2. All final circuits of the location have additional protection by means of an RCD in accordance with Regulation 701.411.3.3
3. All extraneous conductive parts of the location are effectively connected to the protective equipotential bonding according to Regulation 411.3.1.2.
The effectiveness of the connection of extraneous conductive parts in the location to the main earthing terminal may be assessed, where necessary, by the application of Regulation 415.2.2 (R≤50V/I[SUB]a[/SUB]).
When carrying out an EICR, upon entering a bathroom the first test to be carried out is one to establish whether or not there are any extraneous conductive parts within the location. The result measured between any metallic pipework and/or structural metalwork and the main earthing terminal should be above 45kΩ (some are happy using the figure of 22kΩ) to establish that the part is not extraneous. If any metallic pipework and/or structural metalwork is found not to be extraneous then it does not require bonding of any kind. If you have established that there are extraneous conductive parts, the next set of tests are between each extraneous and between each exposed conductive part to the main earthing terminal. The value you are aiming for to determine an effective connection between the main earthing terminal and an extraneous conductive part is around 0.05Ω, this does not take into account any length between the main equipotential bonding connection and the place upon that extraneous conductive part where you are carrying out the test. A 10mm bonding conductor will be within 0.05Ω up to 27m (it is reasonable within an average sized property to get a reading within 0.05Ω from the point of testing back to the main earthing terminal as copper pipe has a larger csa than that of a 10mm conductor). From the point at which you test an extraneous conductive part back to the main earthing terminal you will establish an effective connection to earth by the application of R≤50V/I[SUB]a[/SUB] where I[SUB]a[/SUB] is the operating current of the highest rated protective device serving a circuit within the location. This also applies to any exposed conductive part.
If the resistance between each point tested and the MET is less than or equal to 50V/Ia then each point is effectively connected to earth. For the purpose of this discussion I shall assume that in every case all final circuits of the location comply with the requirements for automatic disconnection. If the circuits within the location have 30mA RCD protection then no supplementary bonding is needed.
If all circuits within the location do not have 30mA RCD protection then a test between each simultaneously accessible exposed and extraneous conductive part should be carried out. The resulting resistance between any two simultaneously accessible exposed or extraneous conductive parts should be equal to or less than 50V/I[SUB]a[/SUB] (which given the measurements taken which have already ascertained that each part is effectively connected to the main earthing terminal using this equation, is highly likely). If the results are within this value, then it can be assumed that supplementary bonding is in place and this particular section of the installation be given a C3 as a 30mA RCD should be recommended.
Now, if the resistance between one or more exposed and/or extraneous conductive parts tested and the main earthing terminal is greater than 50V/I[SUB]a[/SUB] then an effective connection between those parts to earth has not been established (it is easily possible to have an extraneous conductive part that is connected to the main equipotential bonding but just not effectively [say for example 100Ω is measured between a radiator and the MET and plastic pipe feeding the radiator is visible]). We now know that this part should be supplementary bonded because it is extraneous but not effectively connected to earth. A test between this part and all other simultaneously accessible exposed and extraneous conductive parts can be carried out to ascertain whether or not supplementary bonding is already in place by applying R≤50V/I[SUB]a[/SUB] (although at the same time as carrying out this test we can safely assume it is not).
Regardless of whether or not all circuits in the location are protected by a 30mA RCD, this particular section of the installation must be given a C2 because of the lack of required supplementary bonding. Remember, supplementary bonding can only be omitted when all three of the above listed conditions are met.
If the bathroom does have 30mA RCD protection then this in particular warrants no code even though the lack of required supplementary bonding to a non-effectively connected extraneous conductive part has already been given and still warrants a C2. If the bathroom does not have 30mA RCD protection then as stated in one of the previous paragraphs, a C3 must be given (additional protection by way of a 30mA RCD is recommended). This again is in addition to the C2 for lack of required supplementary bonding. Addition of a 30mA RCD covering all circuits in this location will make no difference to the C2 that must be given for lack of required supplementary bonding.
I feel I must make this point absolutely clear: During testing and inspection or installation, if within a location containing a bath or a shower an exposed and/or extraneous conductive part is not effectively connected to earth (see above on how to determine an effective connection) then the existence/addition of a 30mA RCD does not absolve the inspector/installer of any responsibility to code the lack of supplementary bonding/install supplementary bonding to that part!!!
This is, always has been and always will be my stance on supplementary bonding within a location containing a bath or shower. This is as written in black and white in BS 7671 and I will not bend, break nor falter from this stance unless someone can prove beyond all doubt that my stance and that of BS 7671 is completely, utterly and totally wrong!
Now, time for a beer... or ten!