I wasn't querying any of your excellent post :smiley2: merely trying to point out to the OP that the situation may be satisfactory.Refer back to my previous post and point 2 Geoff
That is correct - Ia for the highest rated opd on the circuits of the location.The result measured has to be less than or equal to 50V/Ia
Not so.or 50V/I(delta)n in a.c systems. However, if you were using 30mA as your I(delta)n and using a resistance of 1667ohms as your reference then I would argue that those two parts are not effectively connected to earth and would need supplementary bonding.
Not so.0.05 ohms is a quoted and suggested figure to ascertain an effective connection to earth,
Not so - see above.anything greater than that in a bathroom would require supplementary bonding.
Not really - as above.Only once you have provided supp bonding can you apply the aforementioned formula.
That's what I said.If you are in a bathroom measuring 1.5kohms between a tap and the light swtich then at least one of those parts is NOT effectively connected to earth,
Well, it would but the situation isn't going to arise where you find 1665 or 1668Ω but if the measurement was slightly above the required maximum then an RCD (on ALL circuits AND other conditions) would remove the need for supplementary bonding.therefore just adding an RCD at 30mA would not be enough.
But supplementary bonding is not about ascertaining the effectiveness of a connection to earth.Ascertaining the effectiveness of a connection to earth in a bathroom isn't as simple as just using R=or<50V/I(delta)n. Those are the only points I was trying to make.
Well, obviously it CAN and WOULD BE but it is not an upper limit.0.05 ohms is a stated value that CAN be used to ascertain the effectiveness of a connection between an extraneous conductive part and the MET
First you measure between all the extraneous and exposed parts.If there is no supplementary bonding, how can you use the formula for ascertaining whether or not a supplementary bonding connection is suitable?! You need to first assess the effectiveness of an exposed or extraneous conductive part's connection to earth.
That's what I said.
1666 is just a nominal value obtained from 50/0.03. It is unlikely to be that high.
Well, it would but the situation isn't going to arise where you find 1665 or 1668Ω but if the measurement was slightly above the required maximum then an RCD (on ALL circuits AND other conditions) would remove the need for supplementary bonding.
But supplementary bonding is not about ascertaining the effectiveness of a connection to earth.
(That should have been done already with the main bonding and effective cpcs.)
It is about ensuring minimal potential difference in the event of a fault.
Well, obviously it CAN and WOULD BE but it is not an upper limit.
0.05Ω is only 3m of 1mm or 11m of 4mm conductor so not likely to be achieved anywhere.
That's what I said.
1666 is just a nominal value obtained from 50/0.03. It is unlikely to be that high.
Well, it would but the situation isn't going to arise where you find 1665 or 1668Ω but if the measurement was slightly above the required maximum then an RCD (on ALL circuits AND other conditions) would remove the need for supplementary bonding.
But supplementary bonding is not about ascertaining the effectiveness of a connection to earth.
(That should have been done already with the main bonding and effective cpcs.)
It is about ensuring minimal potential difference in the event of a fault.
Well, obviously it CAN and WOULD BE but it is not an upper limit.
0.05Ω is only 3m of 1mm or 11m of 4mm conductor so not likely to be achieved anywhere.
First you measure between all the extraneous and exposed parts.
If the values are below 50/Ia then either the parts are already bonded (elsewhere) or do not require bonding.
If the values are above 50/Ia then the parts require bonding unless ALL circuits (AND the other conditions are met) are protected by RCDs.
Not so.If the values are above 50/Ia then the parts require bonding full stop! It is irrelevant whether or not an RCD is used.