When rich posted that he disconnected the Main earth when doing the 23Kohm test I asked why and understand why he did, but on thinking this over not sure if perhaps it is the right course.
We disconnect the main earth conductor for a Ze in order to prove an external earth path without parallel paths, but like a measured Zs I think that measuring a piece of metal work to prove it's an extraneous conductive part should be done with these paths in place. Because in my mind to prove this metal is an ECP should be done when the installation is "As-Is" not "How-Should" be.
I've argued this before, on here and off, when told a Zs should be calculated and not measured because of parallel paths, but my answer always is, You only get an electrical fault when an installation/circuit is LIVE, and I therefore when it is in use. So I want to know the condition and therefore the value of the Zs when the installation is in use. When a fault happens, the installation/circuit don't say hold on a second lads I need to disconnect all these parallel paths and make sure I can trip the OPD without them.
Yes I agree that perhaps 2 years down the line something can change within the installation, say removing a metallic service to a non metallic one, and those paths are removed, but I have never advocated designing an installation/circuit to rely on parallel paths, but it should be designed to trip the OPD without the paths. In my view these paths are literally a bonus.
So therefore the same with an ECP, I personally think by removing the main earth and those parallel paths your giving the installation a "false" state. The reason we do bond is to bring all these metallic services into the zone at the same potential. by removing your major source of earth aren't you removing your main reference point?