zap
-
Hi Guys,
I was going to use the following as a part of my assessment with niceic next month but I'm at a quandary.
The job was to swap a spurred socket outlet with a FCU and spurr off that to two double sockets, one next to the FCU in the hall and the other in the living room on the other side of the wall to which the first was installed.
I've upgraded the earthing conductor to a 16mm² and the main bonding conductors to 10mm² except for the water services.
I tested from a disconnected main bonding conductor at the MET to the water stop cock valve body and the highest measurement attained was 0.04 ohms. This figure seems too low (6mm² and at least 10m long possibly more) and leads me to believe a parallel earth path exists. Also the conductor has green (not g/y) insulation and is 6mm² (should be 10mm²).
Here's my issue: The kitchen has been fitted impressively. I mean all the pipes etc. were jointed after the units were installed. Perfectly formed, circular holes in the back of the sink cupboard. I've never seen such impressive workmanship.
I know, now, that I shouldn't have installed the extra sockets until the earthing arrangements were upgraded but that's history.
The owner of the property is not happy for me to start destroying his lovely kitchen and I'm reluctant to do so. Can I record a limitation?
I'll be very grateful if any of you can help.
I was going to use the following as a part of my assessment with niceic next month but I'm at a quandary.
The job was to swap a spurred socket outlet with a FCU and spurr off that to two double sockets, one next to the FCU in the hall and the other in the living room on the other side of the wall to which the first was installed.
I've upgraded the earthing conductor to a 16mm² and the main bonding conductors to 10mm² except for the water services.
I tested from a disconnected main bonding conductor at the MET to the water stop cock valve body and the highest measurement attained was 0.04 ohms. This figure seems too low (6mm² and at least 10m long possibly more) and leads me to believe a parallel earth path exists. Also the conductor has green (not g/y) insulation and is 6mm² (should be 10mm²).
Here's my issue: The kitchen has been fitted impressively. I mean all the pipes etc. were jointed after the units were installed. Perfectly formed, circular holes in the back of the sink cupboard. I've never seen such impressive workmanship.
I know, now, that I shouldn't have installed the extra sockets until the earthing arrangements were upgraded but that's history.
The owner of the property is not happy for me to start destroying his lovely kitchen and I'm reluctant to do so. Can I record a limitation?
I'll be very grateful if any of you can help.