keniff
-
Isn't adiabatic for main earthing conductors and cpc? Didn't think you could use that for bonding?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Bonding water services in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Correct, so on a TN-S system to size a bonding conductor the main earthing conductor must be sized correctly. The OP said he just whacked in some 16mm but I would bet he gave this very little thought. The amount of times I've actually put in a 16mm MEC in a domestic situation because of requirement I could probably count on one hand.
Chances are, the original 10mm MEC was absolutely fine. If so, he could leave the 6mm main bond in place.
why not bond across all of your boiler pipes, including water, make a note on the cert
Err..... 542.3 :angel_smile:
Isn't adiabatic for main earthing conductors and cpc? Didn't think you could use that for bonding?
calculate the min. size required for main earth using adiabatic equation. then the bonding needs to be > or = to 50% of that
As far as I'm aware, the minimum CSA for bonding conductors is 6mm² for TN-S earthing systems.Thanks for all your suggestions. I have several balls in the air at the moment and unable to sit in front of my computer.
It's a tn-s system.
I haven't checked the conductor resistance yet but I will a bit later when I've dropped some of the balls.
Use the time from the time/current graphs in the appendix. This will make your calc more accurate.
As far as I'm aware, the minimum CSA for bonding conductors is 6mm² for TN-S earthing systems.
TN-C-S systems require 10mm².
When you conduct the adiabatic equation, you either use measured values and the disconnection times for those measured values.
Or use those from the tables in appendix 3, not a mish mosh of the two.
As far as I can see, the current required for a 100A BS1361 fuse to operate within 5 secs is 630A, 889A would cause operation within about 1.5secs.
As you haven't supplied the information as to the rating or type of device, a BS1361 100A fuse is most likely the worst case scenario.
Either use the tabulated value of 630A along with the time 5secs, or use the measured value of 889A and the time of 1.5secs.
Using 889A and 1.5secs will result in an earth conductor CSA of 7.6mm².
Using 630A and 5secs will result in a CSA of 9.85mm².
Bonding conductors are required to be half of the CSA of that required for the earth conductor.
Either half of 7.6mm² = 3.8mm², or
half of 9.85mm² = 4.925mm².
In any event 6mm² is more than sufficient.