No waffling, going to get straight to the point. Main water on the exterior of the building in plastic. Changes to copper inside the building. According to regs doesn't need main bonding. Incomer to building is 120mm SWA, TNS with a 70mm earth. Current bonding to the water is 10mm but as said according to the regs it's not needed. Many water heaters & showers on the installation so when an insulation resistance test was carried out between the MET & the stop cock it was showing a dead short. As main bonding isn't required but there is still resistance between the pipework & the MET should there just be supplementary bonding & if so does that mean 6mm would be sufficient.
 
I take it you measured with the bonding disconnected?
There are a few other ways a pipe can be connected though to earth ,via boiler or cylinder CPC ,or via a gas bond if there is one.
Try a low ohm test to give you a clue .
If with all parallel paths disconnected it's less the was 23 K ohms I would bond it.
 
I take it you measured with the bonding disconnected?
There are a few other ways a pipe can be connected though to earth ,via boiler or cylinder CPC ,or via a gas bond if there is one.
Try a low ohm test to give you a clue .
If with all parallel paths disconnected it's less the was 23 K ohms I would bond it.
Yes tested with bonding disconnected. With all parallel paths disconnected the reading is <999 so no main bond required. So as I said is only supplementary bonding required. Also if I'm testing to see if it needs to have a main bond surly I only need to do an insulation resistance tests?
 
One minute you have a dead short then you have <999?
Sorry greater than 999, that what it says on the meter. If you read what I said, with all parallel paths disconnected there is no read but with them connected it's a dead short, which is what you would expect. My only question is does it need a main bond or would supplementary suffice.
 
Sorry greater than 999, that what it says on the meter. If you read what I said, with all parallel paths disconnected there is no read but with them connected it's a dead short, which is what you would expect. My only question is does it need a main bond or would supplementary suffice.

Unless you can't meet disconnection times why would you need supplimentary bonding ?
Why wouldn't I need supplementary bonding even if disconnection times are met? So it's ok to have no main bond because the water supply is plastic and no supplementary to the copper pipe work inside even though with all accessories connected there is a path between said pipe work and the MET?
 
are there more than 1 items of conductive parts that you want to prevent from different potentials ?this is what supplimentary bonding is usually for in my experience , whether it needs main equipotential bonding is another mattter,you have said it was a dead short but also stated its over 999 i guess you mean Meg Ohms?.
if its able to intoduce a potential (usually earth potential) you would need to bond it with a suitably sized cable to the met.
 
are there more than 1 items of conductive parts that you want to prevent from different potentials ?this is what supplimentary bonding is usually for in my experience , whether it needs main equipotential bonding is another mattter,you have said it was a dead short but also stated its over 999 i guess you mean Meg Ohms?.
if its able to intoduce a potential (usually earth potential) you would need to bond it with a suitably sized cable to the met.
Only the pipe work no extraneous. I suppose the question I should have asked is is any type of bonding required if no main bond is needed even though there are water heaters and showers in the installation which will mean the pipe work will be connected to earth?
 
Why didn't you say this in the first place?
I am carrying out an EICR.................................................................................
Wanted to see peoples responses. This a commercial site. I understand that because the service is provided in plastic above ground it is insulated from earth & I have tested to prove that. The internal pipe work is all copper & with all accessories connected under fault conditions it could become live. Not all circuits have 30mA protection so supplementary bonding is required, yes? No? But is that the case if no main bonding is required? I also know if main bonding isn't required we don't put it in because it could create a potential difference but if through the earth of accessories the pipe work could become live should it have a bigger earth back to the MET than what is in the flex. I may be over thinking this as the pipe work may not be at a potential difference & if disconnection times are met & it's a TNS it should all be good but should the main bond that is there be removed or have I just answered my own question?
 

Reply to Bonding 😣 in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

If you can see a piece of plastic entering from the ground then (as cliff said), it does not need main bonding. I think (not sure) this is reg...
Replies
3
Views
379

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top