Bonding | on ElectriciansForums

Discuss Bonding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

C

chronyx

I have done a P.I.R./C.o.S.R on a commercial unit and could see no earth tags on exposed pipework.

The incoming water supply pipe is plastic and therefore not introducing earth potential.

I checked using a long lead between the pipes, sink, and taps and there was no continuity to earth.

Am I therefore correct in assuming this meets the regulations?

Also the main earth conductor has been split into two to go into the M.E.T. in the isolator. Pic attached. I assume this is frowned upon?!

Cheers guys.
 

Attachments

  • [ElectriciansForums.net] Bonding
    CIMG2067s.JPG
    388.9 KB · Views: 109
As long as you feel that the connection complies to regulation 526.1 then leave, though with it just "floating" around I would try to fix it to the case.

When you tested did you perform a continuity test or an insulation resistance test? Was any of these pipes, sinks etc in a special location? Is there any additional protection by RCD ? What was the Zs results like
 
Fixed or no,the oxidised conductors paint a sorry picture
[ElectriciansForums.net] Bonding

[ElectriciansForums.net] Bonding
 
As long as you feel that the connection complies to regulation 526.1 then leave, though with it just "floating" around I would try to fix it to the case.

When you tested did you perform a continuity test or an insulation resistance test? Was any of these pipes, sinks etc in a special location? Is there any additional protection by RCD ? What was the Zs results like

Thanks for your replies everyone, it's really useful to get another spark's opinion on something like this.

I did a low-ohms not insulation resistance, and there are no special locations just a small kitchen area and W.C. RCD times were very good, and it is a split load board with only the following circuits on the non-RCD side:

Smoke Alarm
Lights (Main Office)
Lights (Toilet/Extractor/Disabled Toilet Alarm)
Security Alarm

Having these non-RCD protected seems logical to me as you don't want these circuits affected by nuisance tripping.
 
you need to IR test at 500v between MET and pipework. if the reading is >22k ohms, then no need to bond. the non-RCD circuits are only non compliant with current regs id cables buried<50mm deep without earthed mechanical protection
 
Last edited:
Thanks telectrix, where did you get that figure? I have GN3 and On-site Guide but don't remember seeing it. Always handy to know where to look!
 
Thanks telectrix, where did you get that figure? I have GN3 and On-site Guide but don't remember seeing it. Always handy to know where to look!

The test is described in Guidance Note 8 and is derived from 230V, 10mA as the 'let-go threshold' and 1000 Ohms as the impedance of the human body.
 
Thank you IQ, I didn't get a notification of your reply so I'm sorry for my delay! Much appreciated as I don't have GN8.

What is your take on the split M.E.C's?

There is another one in a D.B. and to be fair I can't see how else they could have terminated it.

But regs is regs, and I have to cover myself!
 

Attachments

  • [ElectriciansForums.net] Bonding
    mec.jpg
    24.1 KB · Views: 38
Thank you IQ, I didn't get a notification of your reply so I'm sorry for my delay! Much appreciated as I don't have GN8.

What is your take on the split M.E.C's?

There is another one in a D.B. and to be fair I can't see how else they could have terminated it.

But regs is regs, and I have to cover myself!

Not sure what IQs take on it would be but mine is that I can not see any problem with doing it. I rather get a good mechanical sound termination by spiting the core conductor this way than trying to fit an oversize CSA into a small terminal, or even worse IMO shaving of cores to make it fit.

As long as the conductors are tight in the terminals I would be happy

Most modern CU take into account the larger earth/bonding CSA sizes so this type of situation will be gradually be phased out over the years.
 
Last edited:
you can buy attachments for the earth bar, which terminates into 2 terminals, and has a tapped thread so you lug onto that. Looks nmuch more proffessional than splitting the cores
 

Reply to Bonding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
916

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top