Ok chaps, so why do we bond lightning conductors???

I've asked quite a few people not one of which has got the foggiest?! Seems idiotic to me :confused:
 
Lightning conductors are tied to earth.

I can understand the reasoning, so there can't be a potential between two earthed items. However bonding in a house won't be rated to take a lightning strike?
 
Lightning conductors are tied to earth.

I can understand the reasoning, so there can't be a potential between two earthed items. However bonding in a house won't be rated to take a lightning strike?

I know that, I just don't understand the advantage of introducing your entire earthing system to a lightning conductor that is already earthed.
 
A nearby earth fault may instigate a rise in potential within the lightning rod with respect to other conductive systems within the property. The point of bonding is to minimise such differences in potential within the property. Ligtning rods are typically installed externally but will still form part of the property's systems.

Sent from my HTC Sensation using Tapatalk
 
Extraneous or not, does it not strike you as odd. Imagine during a lightning storm a bolt hits your bonded lightning conductor at the same time you happen to be in the bath! mmmm, toasty!

perhaps that's why we don't supp.bond baths any more.
 
A nearby earth fault may instigate a rise in potential within the lightning rod with respect to other conductive systems within the property. The point of bonding is to minimise such differences in potential within the property. Ligtning rods are typically installed externally but will still form part of the property's systems.

Sent from my HTC Sensation using Tapatalk

I'm fully aware of the reasons for equipotential bonding. Just not like I said introducing your entire earthing system potentially to millions of volts!
 

Reply to Bonding in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
813
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

  • Question
Thats a freak accident though, it could just as easilly been anything that killed him. It could very well have been a double insulated bench...
    • Like
2
Replies
27
Views
2K
I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
442

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top