The metallic part can be assumed not to be an extraneous-conductive-part if the following condition is met:
Rcp> (Uo/Ib) - Ztl
where,
Rcp is the resistance between the conductive part and the MET in ohms
Uo is the nominal voltage to Earth in volts
Ib is the value of current through the body in amperes that should not be exceeded. (The value may be taken as 30 mA for a disconnection time of up to 0.4 s, as given in DD IEC/TS 60479)
Ztl is the impedance of the human body in ohms. The value suggested in DD IEC/TS 60479 is 1000 ohms where Uo is 230 V (50 Hz) under dry or wet conditions.
Taking Ib as 30 mA and Ztl as 1000 ohms (as suggested above where the disconnection times in the installation are 0.4 s or less and Uo is 230 V), the limiting value of Rcp is given by:
Rcp > (230/0.03) - 1000
Rcp > 6667 Ohms (This is often seen rounded up to 7k Ohms in NICEIC documents)
Thus, if Rcp exceeds 6,667 ohms, the pipe may be considered not to be an extraneous-conductive-part, such that main bonding of the pipe is not required.
Traditionally most electricians prefer to use a 10mA value of current through the body (the Let-go limit) that should not be exceeded, which would change the outcome of the formula to 22k Ohms. To make things more simple the impedance of the human body can be ignored, giving a conservative 23k Ohms, this is the recommended value advised in Guidance Note 8.