Had a couple of run ins with gas fitters in recent times, y'know those guys known to chop bonding off and fling it away if it's in their way in the not so recent past... but suddenly if theres not an earth clamp <600mm from the gas meter you've got gas fitter histrionics

One recent one I'd passed on a EICR where the gas pipe was bonded just after it passed through the external wall, with the gas meter ~ 15M of externally clipped pipe away.

Another, I'd bonded the gas where it entered the house.. the gas meter was 50 feet away in a separate, small freestanding structure, with the pipe buried in the ground.

The point of the bond is create an equipotential zone within the premises, and in both examples the service is bonded at its origin within said premises. Is the gas meter that relevant?

The joke is the gas fitters only interest/test is he has a "earth clamp and bit of wire" box to tick on his safety checklist.. what the wire does is of no interest! I told one to put a clamp on himself and tick his box if it bothered him so much but seemingly it wasn't so much at that point!

Thoughts?
 
The gas fitter probably has no idea what the bond is actually for, and you're the one conducting EICRs. It's your judgement, so tell him to do one.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Main Earth bond with remote meter
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
Teddy Lop,
Last reply from
brianmoooore,
Replies
1
Views
88

Advert

TrueNAS JBOD Storage Server

Back
Top