Can you help me please I have just changed cu old wylex to dual rcd board when I test the rcd trip times on one circuit both rcds trip at 123 x1 and 40 x 5 this is a ring main circuit 32amp
I have left cu off till morning be safe prob be ok when I do rest of checks but scratching my heasd at the mo
 
Hello Guys
Can you help me please I have just changed cu old wylex to dual rcd board when I test the rcd trip times on one circuit both rcds trip at 123 x1 and 40 x 5 this is a ring main circuit 32amp
I have left cu off till morning be safe prob be ok when I do rest of checks but scratching my heasd at the mo

Have you got neutral bars split correctly at cu 1 from each RCD?

You could also possibly have a borrowed neutral possibly on stair lighting circuit.
 
Easiest test is run continuity between all the circuits, i.e take neutral from circuit A and test against circuit B and so on, time consuming but should reveal that you have shared phase/neutral....then you need to find where it is.

Where I stated circuit A and B. A is from a circuit on RCD1, B is from a circuit on RCD2 side
 
Easiest test is run continuity between all the circuits, i.e take neutral from circuit A and test against circuit B and so on, time consuming but should reveal that you have shared phase/neutral....then you need to find where it is.

Where I stated circuit A and B. A is from a circuit on RCD1, B is from a circuit on RCD2 side

Hi there,
Came across this and thought this might help me.So from CU connect to neutral circuit A with wander lead and then go round whole house and see if its common against A and B.Repeat and do with phase.
Understanding correctly ?
To help find fault could you disconnect all fasia sockets and go from one to another ? so you could identify the route of the ring .Connect neutral and phase together with socket removed and just do a continuity at next suspected socket on one of the cable in the box ,and so on and so on.This will then give a clearer idea as to where the route might have become broken or bridged and what floorboard to remove.
Fault finding is the challenge

Cheers
 
No, just IR test between a circuit N on RCD A across to a circuit N from RCD B.

You could also blanket test to start with between the 2 N bars to see if it is a borrowed N.

It should read clear.
 

Reply to both rcds trip on a dual rcd in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
904

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top