dining room light suddenly started blowing the lighting breaker in the house.
I’ve had the boards up and can’t see any shorts in the wiring. It happens even when the light fixture is removed.

Flick switch, breaker blows.

Looking for what to try next to be honest.

Any help greatly appreciated.
Lee
 
Power off. Have a look behind switch… check for damage…

Symptoms suggest a dead short either L to N or L to E on the switched live between the switch and light.


Can we get an idea of age and condition of the installation? Any evidence of rodent damage?
 
Power off. Have a look behind switch… check for damage…

Symptoms suggest a dead short either L to N or L to E on the switched live between the switch and light.


Can we get an idea of age and condition of the installation? Any evidence of rodent damage?
Hi.

Thanks for the response.

The installation is 20-25 years old. I didn’t see any signs of rodent damage on any of the cables. I’ll take another look this afternoon and locate the switch wiring as it’s pretty tricky to get to.
 
20 odd years old, it should be just a circuit breaker. No requirement for rcd protection at that time of install.

Is there any fixtures directly above the switch? Such as a shelf screwed into the wall or maybe just a picture hook?
Is there more than one switch for the same light?



An electrician on site would be able to test the cables in a sequential manner to narrow down where the fault might lie… and be able to repair without too much upheaval.
 
20 odd years old, it should be just a circuit breaker. No requirement for rcd protection at that time of install.
Requirement or not, I've not installed a domestic lighting circuit without RCD protection for double that.
 

Reply to Help with light blowing breaker. Not newly fitted. in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
912

Similar threads

My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
344
Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
447

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top