wade88

Hey guys,

Can someone help me get my head around breaking three phase down into three seperate circuits please.

If i wanted to break down a three phase N + E SWA for example, into three seperate 20amp commando radials say, how would i do this when i only have one N and one E but three circuits?
 
You are creating the 3 circuits from L1+N+E, L2+N+E and L3+N+E. On the neutral (and possibly earth in the event of a fault) you will have all 3 phases present (but 120 Degrees out of phase with each other). So you will wire your DB and take the L1, L2 and L3 to each of the circuits in turn.
 
I understand the first part Topquark, What i cant understand is how i take a N and E with each circuit when i only have one of each. I know this sounds ridiculous but im not so good with three phase and want to understand it.

Let me try and draw it so i can alleviate the confusion...prepare yourself
 
preparing myself ... in the meantime:

You just take the supply into a Neutral Bar and Earth Bar and take a feed for your circuit from there (possibly via a safety device(s), depending on your requirement for multipole safety). It's not really any different (from a purely mechanical perspective) to single phase.
 
[ElectriciansForums.net] Breaking down three phase

Is that too small? But am i on the right lines there so to speak and just repeat for each circuit?
 
Yep. Repeat for each circuit. Main concern would then be balancing current demand across the phases.

As you're providing for 20A from each circuit, your phases would be roughly balanced (assuming the current draw was similar).
 
No worries. You should also connect the L1, L2 and L3 in sequence of rotation (I'll mention it now as it won't complicate the scenario ... just before someone comes in and "corrects" it ;) ).

With using phases individually that's pretty much it.

If you have machinery that uses all 3 phases then you have to worry about using the phases connected in sequence (often called roation).
 
Why is that important to connect them in sequence quark? By this i gather you mean, L1 first L2 second etc. As the circuit is dead whilst installing of course, why would it make a difference?
 
Sorry Wade88 that wasn't very clear. I wasn't suggsting that you connect them in that order (although it does read like that). You connect the cables so that, in the DB, Phase 0deg is on L1, Phase 120deg is on L2 and Phase 240deg is on L3.

It's convention. You normally connect to L1, L2 and L3 in phase sequence so that anyone taking a 3 phase circuit from your DB can easily connect the phases in the correct sequence. This is typically for a motor, so it's important to get the phase sequence/rotation correct.
 
This would be a live test. You need a meter capable of indicating the phase rotation. I use a fluke T140 voltage indicator; it can indicate the phase rotation (ie which comes first) between two phases. So you just do a number of comparisons in order to ascertain the order. There are more expensive devices that will test all 3 phases at the same time etc.
 
Yes i have a T140uk also, (R1) indicates L1 is L1 and L2 is L2 and (L2) indiciates that L1 is L2 and L2 is L1 correct? or something like that. So after the test, if i have determined that L1 is L1 etc, i can denote that L1 is 0 degrees, L2 is 120 degrees and L3 is 240.
 
You'll see it has two LEDs on it marked R and L. R will be lit when you have L1 and L2 in the correct rotary sequence, with the lead on L1 and the meter on L2.

It doesn't (yet) mean that you have identified L1 and L2, it means that the phasing is L1 first L2 second. It could be that you have L1 and L3 at this point. You will need to do a further test to confirm which you had (and another to confirm the correct overal sequence is safest, as someone may have given you two Phase120's and a Phase240 to play with, so be warry).
 
You'll see it has two LEDs on it marked R and L. R will be lit when you have L1 and L2 in the correct rotary sequence, with the lead on L1 and the meter on L2.

It doesn't (yet) mean that you have identified L1 and L2, it means that the phasing is L1 first L2 second. It could be that you have L1 and L3 at this point. You will need to do a further test to confirm which you had (and another to confirm the correct overal sequence is safest, as someone may have given you two Phase120's and a Phase240 to play with, so be warry).
If someone would care to check the manual, I have a feeling that it does if R is lit!
 
I lost the manual for mine, but just checked the downlaodable one from fluke website and you are correct...so was I, in a back handed sort of way. makes a change.
 
One other quick thing quark, if i was to use a three pole breaker, the process would be no different would it, i would just be isolating all three circuits from one breaker instead of three seperate mcbs.

Im afraid i have to ask these no brainers to be sure to be sure...as some Irish fella said
 
NO!.each single phase circuit must have it's own individual breaker, so as to be able to isolate 1 circuit without isolating all 3
 
NO!.each single phase circuit must have it's own individual breaker, so as to be able to isolate 1 circuit without isolating all 3

^^^^^ As telectrix has said each circuit must be isolatable individually. The only time you would use a 3 pole device is if it was feeding one (3 phase) circuit.
 
So i can pop that 3 pole out and replace it with 3 single pole mcb's as we have gone through above and convert it to 3 seperate circuits etc. cool cool. Thanks lads
 

Reply to Breaking down three phase in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
Agree with Dave disconnect unused Phases on the outgoing side of the isolator. No reason to replace mcbs with single pole, unless you need room...
Replies
2
Views
1K
  • Question
Thank you for the advice; I did figure it would be in the realms of discovering, say, a 10mm earth cable in a property, and having no more...
Replies
2
Views
759
That won't solve the problem, you have a TNCS supply with a Ze which has gone out of spec for an unknown reason. You need to get the DNO or...
Replies
24
Views
4K
davesparks
D
  • Question
Why not fit a self contained SPD fed directly from the Henley blocks, and free up a bay? Could probably make one up from whats there, using a...
2
Replies
47
Views
4K
  • Question
You will need to now if there is start up current on the equipment. To choose what type of mcb / rcbo B C or D .Also Just wondering if 16amp...
Replies
17
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks