I went to a customer today who told me she had a pre electrical survey done by BG before they would agree to connect a new boiler, the "survey" was done by the sales guy.

Basically she told me that he said BG would not connect the boiler because he did a "socket and see test and he got more than 100 ohms???",he didnt remove any loads or isolate anything whilst doing this test, after getting this reading he promptly went outside looking for an earth rod.

If the guy had the common sense to actually look in the right meter box(he looked in the gas meter box), he would of noticed the supply is a TNCS which was installed in 2001, 35mm tails from the road, 25mm going through the outer walls and into the basement.

I carried out a Zs test on each floor of the house, the results were 2.16ohm, 2.01ohm,1.95ohm and 1.98 ohm all on 32A mcb's, all 3 circuits exceed the OSG max permitted figures,

I then took 5 Ze readings, they varied from 1.05ohm - 1.15ohm so its fair to say its the high Ze which is the problem.

The installation is protected by a 30ma RCD Main Switch, so perhaps this problem was spotted earlier.

I tested the RCD fully and the times come back 17.8ms(x1) and 7.8(x5)

My query is should or can British Gas refuse to connect the boiler to a circuit which is protected by a fully working RCD, when the Zs is averaging 2ohms when the advice the IEE gives to us is that we can safely use circuits on RCD's when the loop well exceeds 21ohms or more.

I have to write a report for the customer and also advice on contacting the DNO so i'd appreciate your valued feedback!!

Cheers
 
Last edited by a moderator:
I put the report in to British Gas and wrote the customer an idiots guide on what to do when the Ze is outside of its parameters, the DNO turned up within 4 hours of the phone call, dug the garden up and part of the pavement and left, returned the next day and sorted the problem, Ze now 0.21ohms, British Gas returning next week to "test again" lol despite my schedule they are sending a salesman with a "socket & see" and an "ohmmeter".
 

Reply to British Gas refusing to connect in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
185
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top