No, you just thought you'd try being a clever dick again!! lol!!
I stated that most of these metermen know less than a electrical trainee. But i can just guess as to what the earth rod installation is like and the sort of Ra value that has been obtained!!
Now if this district heating project has such a high monetary value, there shouldn't be any financial restrictions to actually providing a sub 1 ohm TT system, but will it ever get such a TT installation?? Very doubtful in the UK, after all there is always an RCD to bung in!!
how can you obtain a steady sub 1 ohm reading which you can guarantee not to fluctuate due to weather drying up ? will the circuit meet its 0.2s or 1s disconnection times depending on circuit design?
just a question...
TT does not equal hit a single 3/8" dia 4' rod in the ground, just in case some don't realise that.
how can you obtain a steady sub 1 ohm reading which you can guarantee not to fluctuate due to weather drying up ? will the circuit meet its 0.2s or 1s disconnection times depending on circuit design?
just a question...
In certain areas, subject to ground conditions, it can be done, and very easily. I have done it, as will have any electrician worth his salt. It won't ever have been on a domestic though that's for sure. Last time I did it was at the intake building for a large agricultural installation.
Ten or so underground sub mains fed from the intake position. It was either a decent earthing system or £2k for an up front s-type for the whole complex, which in itself would have been idiotic.
Sorted that for you Damian.I think that's a gross overestimation of most current day electricians knowledge of TT systems Paul. A single 3/8" twig is the only language they speak nowadays.
Start with 2x 5/8"x8' rods spaced 10' apart and then test it and take it from there.
Damian , how did you account for 705.411.1 if it was agricultural ?
Edit ; I have been on the sauce , so may be missing something :49:
Neither the main panel or any of the sub mains it fed were in areas that could be deemed agricultural. There were sub mains elsewhere that fed areas where livestock was kept, therefore 705 would only apply in those areas.