skamuk

My friends downstairs sockets are tripping the RCD. First thing I did is unplug everything on the circuit, switched on the MCB and the RCD tripped. Tested continuity of L-L N-N CPC-CPC between the legs. CPC has no continuity whatsoever. Could anyone advise me what would be my next step to determine where the break in the cpc is? Thanks
 
OK, the CPC being split is highly unlikely to be the cause of your RCD fault, however, here is a very quick way of finding your earth fault.

Get a socket tester (3 neon variety)

Unplug everything from the ring main

Disconnect 1 leg of the CPC at the CU

Go around each socket in turn with the tester, at some point you will go from a fully serviceable ring to a 'no earth' indication. Or vice versa.

Stop and investigate further

Simples
......

I like your style, Sergei.
 
Really? I didn't realise there was a difference between r1 r2 and R1 R2. My bad! What does the capital letter version stand for?

There isn't much of a difference, people just tend to get a little bit muddled up with the terminology :)

r1 is the end to end of the line conductor
r2 is the end to end of the CPC.

R1+R2 is cross connecting the two and testing together.

r1+r2 is a myth :)
 
Really? I didn't realise there was a difference between r1 r2 and R1 R2. My bad! What does the capital letter version stand for?

Only reason we've not got "Gasp..." and "I'm out of here...", is that it's late.

r1 and r2 are end-to-end resistances of ring circuit line and cpc conductors. R1 and R2 are resistance from origin of circuit to furthest point (in the case of a ring, this is the centre) of line and cpc. Not the same thing at all!
 
Oh wow! I didn't know that. Thanks! I'm not an electrician just yet as you have all probably gathered, I'm still at college so I'm learning every day. I have another question, slightly off topic: I was having this debate with my teacher/lecturer... He says that if you have a conductor, say 50m long, and you measure continuity between one end and the mid point (25m) you will get half the ohms value of measuring the full length of the cable. I thought that the extra copper would effect the half way reading? Would the value be half?
 
it should be exactly half. look in the osg, there is a table giving the resistance/m of all the cable sizes in milliohms/m. just multiply that value by the length , dvide by 1000, and that will give the resistance of X metres.
 
Have done this. All connections are present and terminated ok. I now need to determine where the break is, bearing in mind all cpc are twisted together at each socket. Would I untwist all of them and test continuity between each socket?
prove that every point served on the ring has R2 present.....do the adiabatic then move on to the RCD issue...
dont waste time arsin about looking for broken R2...as long as every point served has R2 available...
 
you might get lucky and find that some ham-fisted dork has snapped one when twisting them. and what's the betting he's put 2 in 1 sleeve. aarrggghhh.
 
Just a thought...

Name - Skam UK?
Instrument will test ze but not zs?
Questions simple series resistance of length of cable?

Does the term 'windup' mean anything to anyone?
 
I posted in the general forum because I have a general electrical enquiry. I'm not sure what the definition of 'DIY' is. An electrician, plumber, builder whatever will do their own work themselves? Do it yourself doesn't make sense to me.. I assume it's used here for people who aren't well educated on the subject, which in turn means there will be a lot of blind leading the blind going on there...
 
Electrician and his mate went round there yesterday and after 3 hours of searching, found a damaged length of t&e although I'm not sure where they found it or why it was damaged. Problem sorted though.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Broken CPC on ring final
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
59
Unsolved
--

Advert

Thread statistics

Created
skamuk,
Last reply from
skamuk,
Replies
59
Views
8,601

Advert

Back
Top