broken ring , no continuity on all conductors , whats best way to find the fault?
 
Isolate and lock off
Disconnect all rfc conductors at the CU
locate the sso nearest to the center of the rfc and disconnect all conductors
You now have 2 legs of the rfc separated
Through a process of elimination test for continuity of both legs until you get an open circuit
Carry out this procedure until you eventually find the open point
Simples
Pete999
 
Since you have no continuity on all conductors it is likely the ring is disconnected at a single point (though it could be three different points).
Take all the conductors out of the board, join incoming line and incoming cpc (or outgoing line and outgoing cpc), then go round the sockets testing continuity between line and cpc.
At the point where you stop getting continuity (or start getting continuity) the fault is either at that socket or the one before of the one after, take the plates off and find the disconnection.
 
Since you have no connectivity on any of the conductors, try to work out whether the circuit really is supposed to be a ring or whether it's just a radial branched at the origin. What's the conductor size, and the fuse or breaker rating?

Identify which sockets are served by that circuit by powering on one circuit at a time and checking what's live. No point testing sockets that are on another circuit.

Assuming two cables into one fuse or breaker, disconnect the circuit from the supply. At the origin, connect any two cores of one cable together, say line and CPC. Work outwards from the origin, measuring the resistance between the two selected conductors. Disconnect the cores and repeat for the other cable. Of course, you may have to inspect some of the socket wiring for evidence of spurs and perhaps disconnect some sections and test separately. This should give you a picture of what's connected to each cable and how far from the origin each socket (or other load point) is.

If you're satisfied that you know the layout of the circuit, re-connect the ends to form a ring and re-test to the regs or replace the fuse or circuit breaker with one suitable for the existing circuit arrangement.


Edit: I see, Richard, that we are thinking along the same lines.
 

Reply to broken ring . in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
668
loz2754
L
I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
450

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top