hi guys

after a little advice re a 30 A Type 2 BS 3871 MCB. Now i know they are old but still compliant , just checked the OSG p 49 Table 7.1 for maximum length and installation methods but there not listed.

i have the maximum ZS of 0.88 from page 103 table 2d OSG where they are listed.

can anyone advise where the allowed installation methods would be listed? or are they the same as for a type b BSEN 60898 ?

many thanks
 
I assume you have a spare way on the DB and you are installing a New 30A radial circuit. The requirement is that all new circuits must comply with current edition of BS7671. I cannot find any reference to BS3871 CB's being non-compliant it is in fact an overcurrent device.
Providing the design criteria are met for disconnection time IE Zs is low enough to get 0.4s, the rated short circuit capacity of the CB is not exceeded IE PFC. The Volt Drop is compliant and at 14 metres this all looks Ok.

Your big problem is the circuit needs RCD protection as the cable is concealed so providing you can fit an RCD Adjacent to DB, using the old CB should be Ok. The info for BS3871 has probably been left out of new regs because they are no longer easily obtained having been replaced by BSEN 60898 CB's. So providing you can get the old info on max Zs and it complies then I agree it should be OK. Measure the PFC at the DB compare to the M number on the CB if max PFC is lower than M number - then I don't think it is a problem.
 
thanks platty thats what i thought. the max zs is actually listed in the osg so no problem there when calculated. pfc is well below the 3ka rating of the breaker. RCD is present on the exisiting board, but it is not ideal as it is a rcd mainswitch. so no segregation of circuits, but the property is a bungalowe with only 1 lighting and 1 ring main and a cooker circuit.
 

Reply to BS 3871 Type 2 30 A MCB (allowed installation method) in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
170
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top